  1. #1
    Join Date
    Jun 2013
    Posts
    46

    Skinny line is chilly. No cooling. How bad?

    The outside skinny copper line is cold and gets condensation. I was told the fat line should be cold and the skinny should be hot. The outside unit starts, but I can hear it stop after a few minutes, but the fan keeps going. I called a place and they said it could be a filter somewhere or the compressor may have broken. I'd like some thoughts so I don't get taken to the cleaners. I don't see ice anywhere. Sounds like it might be expensive.

  2. #2
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,039
    Could be worse. It sounds like it is that filter they mentioned. Id recommend not running it until its repaired.

    The next question is what clogged up the filter? That question will be tough to answer . It is a gamble on your part as to how much life the unit has. It could run for years or have another failure soon. It may be worth a shot though.

  3. #3
    Join Date
    Jun 2013
    Posts
    46
    Quote Originally Posted by SBKold View Post
    Could be worse. It sounds like it is that filter they mentioned. Id recommend not running it until its repaired.

    The next question is what clogged up the filter? That question will be tough to answer . It is a gamble on your part as to how much life the unit has. It could run for years or have another failure soon. It may be worth a shot though.
    They said it could be due to installation error by the installer or I think they said valves coming loose in the compressor and clogging the filter, but they'd like to check it out first obviously.

  4. #4
    Join Date
    Jun 2013
    Posts
    46
    Ok, they are coming out next week. Any suggestions/ideas/things to look out for?

  5. #5
    Join Date
    Aug 2001
    Location
    Mechanicsville, Virginia
    Posts
    1,256
    Ask to see the Technicians Credentials. They are in the form of wallet cards.

    It would be nice if they hold a State issued HVAC Tradesmans license, and/or NATE certification in servicing (not only installing) your type of equipment.

    These would be in addition to the mandatory EPA certification to legally handle refrigerants.

    "If perfection is your goal, you may end up with good enough, what might you end up with when good enough is your goal?"
    Wayne Pendergast, efficientcomfort.net

  6. #6
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    701
    Might be time to get some new equiment. How old is the unit? And is it a heat pump? Could be a small problem. Need some more information to figure out what could be wrong.
    Blue Fox

  7. #7
    Join Date
    Jun 2013
    Posts
    46
    No heat pump. Under 5 years old. Thanks.

  8. #8
    Join Date
    Jun 2013
    Posts
    46
    I don't see a little can on the skinny line which someone mentioned could be the cause. It goes all the way into the outside unit with the can.

  9. #9
    Join Date
    Dec 2008
    Location
    Ontario Canada
    Posts
    545
    Quote Originally Posted by cano View Post
    I don't see a little can on the skinny line which someone mentioned could be the cause. It goes all the way into the outside unit with the can.
    Sometimes the filter drier (little can) can be located in tough to see places, try a google search for "refrigerant filter drier" that may give you a better indication of what you are looking for. Even if you found it, it's not something replaceable by a home owner. Did you take a temperature reading of the little line? Or just by feel

  10. #10
    Join Date
    Jun 2013
    Posts
    46
    Oh, I'm not doing this myself. I know what I'm not capable of, just trying to know as much as possible before they come next week. I just touched the line and it was cold and had condensation. From my understanding, the insulated line should be cold and the skinny warm. My other unit which works great is opposite of this one.

  11. #11
    Join Date
    Jun 2013
    Posts
    46
    Just searched for "refrigerant filter drier" and that's what I tried to find on my system, but don't see it anywhere. My neighbor's is right on the line as it leaves the outdoor unit.

  12. #12
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    15,968
    Quote Originally Posted by cano View Post
    Just searched for "refrigerant filter drier" and that's what I tried to find on my system, but don't see it anywhere. My neighbor's is right on the line as it leaves the outdoor unit.
    Might be "inside" the unit, look down inside of it.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  13. #13
    Join Date
    Jun 2013
    Posts
    46
    I was thinking that, but seemed like that would have been a PITA to install. I'll check when I get home. Thank you!

Page 1 of 7 1234567 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event