    Anybody here have Copeland O/L specs ?

    This compressor is a:

    Copeland AFE11C3E IAA 901

    How can I find out the operating specifications of the compressor O/L? Specifically: how many running amps will cause it to open?
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  2. #2
    Join Date
    Aug 2009
    Location
    anaheim
    Posts
    11
    Post Likes

    Overload Specs

    PHM,

    That's a 1/3 HP Nom R404a Sweat R Compressor 115 VAC is that correct??

    If so it takes a P/N 971C10001 Compressor Overload/Protector.

    Copeland doesn't and won't provide the spec you are requesting per se, but the reasoning is sound. The OL/P 'hugging' the compressor senses the compressor heat and the generated amp draw/voltage drop heat together and combines them to provide the protection curve Copeland determines is necessary.

    It's a very efficient and reliable control when used in this application but could be ineffective and unreliable if used as a stand alone component.

    Good Luck, I hope this helps.

    B

  3. #3
    Join Date
    Sep 2002
    Posts
    22,929
    Post Likes
    Thread Starter

    My actual question is this -

    I have a 1/3 HP Copeland compressor as my subject. The FLA is 5.6 The system draws 6.55 amps - with the condenser fan - which is 0.34 amps by itself. So the compressor itself draws 6.2 amps. But the compressor cycles on the O/L. So my question is: is the O/L weak?

    PHM
    -------




    Quote Originally Posted by HVACRACbob View Post
    PHM,

    That's a 1/3 HP Nom R404a Sweat R Compressor 115 VAC is that correct??

    If so it takes a P/N 971C10001 Compressor Overload/Protector.

    Copeland doesn't and won't provide the spec you are requesting per se, but the reasoning is sound. The OL/P 'hugging' the compressor senses the compressor heat and the generated amp draw/voltage drop heat together and combines them to provide the protection curve Copeland determines is necessary.

    It's a very efficient and reliable control when used in this application but could be ineffective and unreliable if used as a stand alone component.

    Good Luck, I hope this helps.

    B
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  4. #4
    Join Date
    Apr 2005
    Location
    AZ
    Posts
    194
    Post Likes
    Well the performance sheet at the highest (140° cond 15° evap) shows 6.7 amps so I wouldn't think it should open at 6.2 unless there is alot of heat or it is weak. And if it is running at those extremes i'd expect its been cycling for awhile and getting weaker.

  5. #5
    Join Date
    Jul 2000
    Location
    Cuenca EC
    Posts
    13,380
    Post Likes
    The rated max continuous current (MCC) for this compressor is 7.84 amps, which is usually what they use to select the trip point for the overload. I'd say you have a weak overload.

    Name:  AFE11C3E-IAA.jpg
Views: 434
Size:  53.5 KB

    Check out Icemeister's Back Room

    Read My Latest Rambling:
    What Is Mechanical Subcooling?

    ...and a new calculator:
    Nitrogen Pressure Calculator

  6. #6
    Join Date
    Sep 2002
    Posts
    22,929
    Post Likes
    Thread Starter
    You were right - I replaced all the start components and it's off and running. Passed the health inspection today so that's about all they cared about. I got them to shut off all the stoves, ovens, grilles, fryers and set the A/C on 68Ί over night. It was 70Ί*in the kitchen at 8:00A this morning, the health inspector came at 9:00A and, what do you know? All the refrigeration equipment was at temp. <g>

    I don't know what they are going to do next month though . . . . <g>
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  7. #7
    Join Date
    May 2013
    Location
    Utah
    Posts
    57
    Post Likes
    Copeland offers an electrical handbook which is very useful to keep on board a service truck or on hand.

  8. #8
    Join Date
    Jan 2004
    Posts
    69
    Post Likes
    Quote Originally Posted by StarCat View Post
    Copeland offers an electrical handbook which is very useful to keep on board a service truck or on hand.
    hard to find these locally I think they are CD's now