Results 1 to 12 of 12
    Jan 2012
    Oregon
    I need to charge a r408 system
    I have a r 408 system that is low on charge. High superheat, low sub cooling, low head pressure and pretty close to normal low side pressure. Is it best to charge by sub cooling or by the sight glass? Thanks Rusty
    Jan 2010
    Don't worry about sub cooling on a refrigeration system. The sight glass needs to be full. Don't rush it though, let the box pull down some first.
    Jan 2012
    Oregon
    So sub cooling isn't a factor?
    Jan 2010
    Not really, it kinda is what it is. Now the super heat is where you need to be concerned.
    Jan 2012
    Oregon
    Ok will do thanks.
    Jan 2010
    What's the possibility of converting it to R404a ? It's a whole lot cheaper then R408. What size system ?
    Jan 2012
    Oregon
    I will get the specs tomorrow and let you know.
    Jun 2013
    Montana
    I don't know if you can convert r408 to 404. But 408 is a replacement for 502
    Oct 2011
    Chicagoland Area
    Did you repair the leak?
    MontanaJon, you can convert it. New oil, drier, suction filter, and figure in a changeout of the drier, filter, and cleaning the txv screen after a week of runtime.
    Jun 2013
    Montana
    2sac- just a question but would the condenser be able to handle the load. I have seen old 502 condensers that would handle a negative evap but not if it was 22. Maybe I am not think all the way. *But I did have a concern about the condensing unit.
    Oct 2011
    Chicagoland Area
    I have read that 404 will increase capacity when replacing 502 @ low temp but have done a number of retrofits, nothing larger than 5hp, without issue.
    Jun 2013
    Montana
    Thanks for the info 2sac. I will keep that in mind.