Results 1 to 13 of 20
    Jan 2012
    Oregon
    Iced up suction line
    Is it normal to have a iced up suction line? The unit is a r408 freezer that is running TXV valves. I just want to make sure it won't hurt the compressor. I'm a newbie and this is the first time I've encountered this. Thanks Rusty
    Oct 2012
    Wisconsin
    Yes you will get ice on the suction line for a freezer, its cold.
    As far as the compressor, check the superheat on the suction line at the compressor. Should be at least 20* superheat at the compressor to protect it from liquid floodback.
    Jan 2012
    Oregon
    Thanks for the help. Should I worry if the suction line ices up all the way back to the compressor?
    Oct 2012
    Wisconsin
    Quote Originally Posted by bigbucks View Post
    The only good way to know for sure is checking the superheat at the compressor. It is normal to see frost pretty close to the compressor, but not a good rule of thumb to go by. All depends on the system, length of lines, etc...
    Think of it this way though, your evaporator temp is well below 0. Even by the time the gas gets back to the compressor it is still below 32* and will create frost.
    If your superheat at the compressor is less than 20*, you want to check at the evaporator(s) for proper superheat and make sure something isn't flooding back.
    Jan 2010
    No, they can be covered with frost.
    Jan 2012
    Oregon
    Ok thanks for the info.
    Mar 2013
    swan valley idaho
    If no frost then line is above 32. If sst is -20 then you would be over 50 super heat. Not good
    So ya almost any walk in freezer should have a frosty line all the way back
    May 2003
    Utah
    Completely true.
    Low temp application running a saturated suction of -20*F with 40* superheat at the compressor inlet. Do the math.....that's a 20*F temperature at the compressor inlet.
    The suction piping, suction service valve and perhaps part of the compressor endbell will have frost on it. So what???? It's a simple indication of a temperature below freezing...nothing more.
    Without checking the superheat you have no idea whether this condition is dangerous (liquid present).
    May 2005
    i had a copeland tech tell me the compressor can be covered in ice..and still be Ok..
    that said, i will set the superheat at the compressor..to protect the compressor..
    Let's give nukes a chance.
    Mar 2013
    Set the superheat at the compressor. there is one id like to see. considering the TEV is at least 1 wall apart from you. =p
    I am a bit baffled as to why an accumulator isn't on it (assuming it has a pretty short run, if you're getting good frost all the way back)
    Also be sure it's insulated with 3/4' or 1''.. otherwise ya, 20-30 SH is on the money. don't let it fall below that.
    May 2005
    i always set compressor superheat, i could care less what the superheat is at the evap, i want that compressor to be protected..
    Jan 2010
    Quote Originally Posted by primmers View Post
    That could start some debate if your including refrigeration.
    May 2005
    if the superheat at the compressor is Ok the case/box is gona be ok.....right?