Cooling a tortilla factory
62 yr. old building, 1768 sq.ft, very very leaky. Tortilla oven puts off an enormous amount of heat as does the deep fryer.
The fryer to cook the chips is for frying donuts so the owner (friend of my family) wants to buy a new fryer and have a new exhaust hood installed.
Also she is looking to repace the main tortilla oven.
There is currently a single 5 ton split system trying to keep up with the heat load....no luck. There are a couple old evap coolers I see....
Equipment she is looking to buy is Model CF-100 hot oil fryer from Superior Food Machinery, Inc. out of Calif...
Here are some pics:Last edited by Steve Wiggins; 03-14-2007 at 06:54 PM.
"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
-
03-14-2007, 01:29 PM #2
Professional Member
- Join Date
- Nov 2000
- Location
- Waco, Texas, USA
- Posts
- 6,153
Can't figure out how to post pics......where did img wiz go?
"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
-
03-14-2007, 02:36 PM #3
Regular Guest
- Join Date
- Sep 2006
- Posts
- 6
-
03-14-2007, 05:25 PM #4
Professional Member
- Join Date
- Nov 2000
- Location
- Waco, Texas, USA
- Posts
- 6,153
.
"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
-
03-14-2007, 05:28 PM #5
Professional Member
- Join Date
- Nov 2000
- Location
- Waco, Texas, USA
- Posts
- 6,153
Ok found it....
"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
-
03-14-2007, 05:30 PM #6
Professional Member
- Join Date
- Nov 2000
- Location
- Waco, Texas, USA
- Posts
- 6,153
.
"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
-
03-14-2007, 05:40 PM #7
Banned
- Join Date
- Dec 2001
- Location
- Southern Tier, NY
- Posts
- 6,066
you need source ventilation/ exhaust for the oven
you can't realistically cool that load
the proper standards are in the American Assoc. of Industrial Hygentist's book
git out your check book, tho
i think my copy was $400
-
03-14-2007, 05:43 PM #8
Banned
- Join Date
- Dec 2001
- Location
- Southern Tier, NY
- Posts
- 6,066
Oh my, things are casual in TX
here in NY...Dept of Health ,
would be lockin' them doors ......
-
03-14-2007, 05:44 PM #9
Professional Member
- Join Date
- Nov 2000
- Location
- Waco, Texas, USA
- Posts
- 6,153
.
"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
-
03-14-2007, 05:49 PM #10
Professional Member
- Join Date
- Nov 2000
- Location
- Waco, Texas, USA
- Posts
- 6,153
Its really a pretty neat little operation.
These people are personal friends of mine.
I am just trying to help them out.
They are even considering abandoning this structure and building a new factory custom from scratch.... That would be fun to design huh?"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.
-
03-14-2007, 07:06 PM #11
Professional Member
- Join Date
- Mar 2001
- Posts
- 1,213
First concern should be fire suppression system. Looks like you got a job ahead of you.
-
03-14-2007, 07:15 PM #12
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,318
Yeah, it odes look like a neat little business. And with most of the un-skilled labor in our country now-a-days buying their products, they probably have a better balance sheet than us HVAC guys so.
If if were me, I would lean towards them building a new place (or find a larger building) outside of town (read that outside of as many governmental jurisdictions as possible).
Is it dry enough in Waco to go mostly swamp coolers? If so, you might get a lot more bang for the buck cooling that way.
It seems to me that with a large % of make-up air, you would need at least a YCH 120 or 150 to cool that place (10-12.5 ton Trane pack). And as dependable as Trane's are, the airborne grease would do it in.
Good luck, and let us know what you do.GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
03-14-2007, 09:53 PM #13
Professional Member
- Join Date
- Nov 2000
- Location
- Waco, Texas, USA
- Posts
- 6,153
I have been given some input and suggestions by the equipment manuf.
1. Fire suppression
2. Hood extensions over hot oil fryer
3. Island hood for oven?
4. Stainless Steel on back wall behind hood/fryer
5. Side induction.....not exactly sure what that is
6. 6" overhang of hood over fryer
26 gallons
335,000 btu @10"w.c.
Pos or neg pressure
212-230°F"And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.