    How are VAV damper controlled?

    Ya, I know, very basic question...

    We got Trane VAV units controlled with Siemen TEC (Terminal Equipment Controller). Looking on the wiring diagram the damper is wired to DO (digital output). When I saw this, I was like, "what?"

    I'm guess it's using some type of pulse signal from the digital output to set the damper position. If so, anyone know the detail of the signal form? How hard would it be to change the VAV to take analog signal?

  2. #2
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,690
    Most VAV controllers with integrated damper actuators use drive-open drive-close actuators (or sometimes called floating control) that pulse the actuator either open or close for a set amount of time (seconds) to achieve the airflow setpoint. It seems to be the industry standard (ones I have worked with: ALC/Alerton/Delta/Reliable/t.a.c. Xenta/Andover) due to probably cost. But it is a good and stable control method, with an analog output you will probably need a PID that is tuned well and then the actuator is going to be making small (lets say 0.1V) adjustments all the time and the output is going to have alot of on time. I haven't seen an integrated VAV controller with damper actuator that is controlled by an analog signal, there are probably ones out there.

    Why are you wanting to change the digital signal to an analog one? Are the actuators part of the board or external?

    kontrol out
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  3. #3
    Join Date
    Oct 2002
    Posts
    48
    Thanks, it makes more sense now. So I guess the position I'm seeing when I use Datamate Base (Siemens) is just an estimate rather than actual feedback.

    I post in another thread that I want to go with an open system using PLC. PLC can use digital output and analog output. I would think analog output would be give better control since the same PID are at work anyway. It seems Trane does make analog VAVs according to their website. I will call them up and see if I can learn more.

    Well, if I can't do it with PLC then I would also look at an open standard VAV controller instead of proprietary stuff.

  4. #4
    Join Date
    Nov 2006
    Location
    CA Central Valley
    Posts
    437
    Analog control is all well and fine, but as kontrolphreak said, it will use a lot more power than a pulse-controlled floating actuator.

  5. #5
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,690
    Some actuators have a true feedback, others as you said calculate the position by adding the time it has pulsed open or closed to give a position. Most actuators are around 90 second runtime, so if you have pulsed it on 9 times at 5 second pulses it should be approx 45 seconds = 50%.

    For floating/drive-open drive-close control I like software that can leave the DO for ON energized at 100% and the DO for OFF energized a 0%. That way whenever it reaches 100% or 0% you know it is truely opened or closed (sometimes the calculations drift over time and it only pulses for a total of lets say 80 seconds so you are not really at 100% open, then when you drive it closed your calculations are screwed aswell). AutomatedLogics old VAV controllers did this, the new ones I don't know about.

    I have never had a problem with this setup and wouldn't change it unless I saw a very good reason to do it.

    kontrol out
    Last edited by kontrolphreak; 03-09-2007 at 01:59 PM. Reason: correcting my math
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  6. #6
    Join Date
    Nov 2006
    Location
    CA Central Valley
    Posts
    437
    Quote Originally Posted by kontrolphreak View Post

    For floating/drive-open drive-close control I like software that can leave the DO for ON energized at 100% and the DO for OFF energized a 0%. That way whenever it reaches 100% or 0% you know it is truely opened or closed (sometimes the calculations drift over time and it only pulses for a total of lets say 80 seconds so you are not really at 100% open, then when you drive it closed your calculations are screwed aswell). AutomatedLogics old VAV controllers did this, the new ones I don't know about.
    Alerton VAV-SDs do this as well.

  7. #7
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,690
    dngrsone,
    Do you work with Alerton? If so can you answer the question I posted here:

    http://www.hvac-talk.com/vbb/showthread.php?t=132224

    kontrol out
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  8. #8
    Join Date
    Oct 2002
    Posts
    48
    Quote Originally Posted by kontrolphreak View Post
    For floating/drive-open drive-close control I like software that can leave the DO for ON energized at 100% and the DO for OFF energized a 0%. That way whenever it reaches 100% or 0% you know it is truely opened or closed (sometimes the calculations drift over time and it only pulses for a total of lets say 80 seconds so you are not really at 100% open, ..
    Thanks, that's what I'm looking for.

    I can easily duplicate that functionality in a PLC using a pair of DO. This way I can use the same VAV and my home brew controller.

  9. #9
    Join Date
    Sep 2006
    Location
    Rhode Island
    Posts
    244
    Quote Originally Posted by lostdude View Post
    Thanks, it makes more sense now. So I guess the position I'm seeing when I use Datamate Base (Siemens) is just an estimate rather than actual feedback.

    It’s true the TEC never really knows where the actuator is in the stroke. But it is very good at knowing where it told it to be. It's also true that over time it gets a little lost. Manually commanding the actuator to the zero position recalibrates the system (no longer lost). Siemens came up with an automatic recalibration procedure that works very well. Once every 12 hours the TEC Manually commands the actuator to zero. It recognizes the zero position then releases it back to normal operation. You have the option of disabling this process or customizing the timing if you wish. The only down side to this recalibration procedure that I have seen is that you get the occasional customer inquiry about his air conditioning going off every day for a few seconds then coming back on.

    All in all the Siemens TEC's have proven to be a very good and reliable controller.

  10. #10
    Join Date
    Oct 2002
    Posts
    48
    Quote Originally Posted by shifferbrains View Post
    ..All in all the Siemens TEC's have proven to be a very good and reliable controller.
    I'm sure TEC is just as good as any other VAV controller. Our system is showing its age in other places as well at DPU panel, BMC, etc... I like to use this oppertunity to move toward an open system without being tied to Siemens Insight.

    I would love to keep the TEC if I can talk to TEC directly via OPC or some standard type of network.

  11. #11
    Join Date
    Oct 2005
    Posts
    322
    For what it's worth, the design engineers say that floating actuators will outlast modulating in a VAV application by a factor of 5 or more.

  12. #12
    Join Date
    Dec 2006
    Location
    Washington, DC
    Posts
    510
    Not sure of all VAV controllers, but the Siemens TEC, Trane UCM and Carrier ComfortID all use floating point control. Out of these three, only the Carrier ComfortID uses a 0-10vdc feedback signal to know damper position. The Trane damper has open/close end switches to stop the signal to the motor once the damper reaches the fully open or closed position.

    At my last company, we serviced a 12 story building with Trane equipment and Seimens 600 controls which had 300+ Trane VAV's with TEC's. They worked great, the biggest issue was motor or gear failures on the dampers.
    Last edited by Balibe; 03-09-2007 at 08:31 PM.

  13. #13
    Join Date
    Jan 2003
    Posts
    539
    Quote Originally Posted by lostdude View Post
    Thanks, it makes more sense now. So I guess the position I'm seeing when I use Datamate Base (Siemens) is just an estimate rather than actual feedback.
    The VAVs that I see usually have some kind of air flow sensor.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event