    R22 or replacement
    Have a flat 10 ton unit already found and repaired leak. What's my best option for refrigerant. I understand there are considerable capacity loss with replacement refrigerants.
    Sent from my DROID RAZR using Tapatalk 2
    Aug 2012
    Capacity loss and need to change oil to poe, and change o rings and possibly txv. I would do a serious pressure test and stick with 22.
    It's not if your doing it right it's whether your doing the right thing that is important.
    The Hot South
    Quote Originally Posted by toocoolforschool View Post
    X2
    Memphis,TN
    MO99 is worth a try I just put it in an older 12.5ton carrier split system and the head runs lower ,suction runs lower, but 20 degree drop across the evaporator. The cost is a lot better than a drum of r-22.
    Oct 2010
    I'd go with r421a if it were mine.
    May 2013
    Utah
    Additional infractions may result in loss of posting privileges.
    StarCat
    Tucson, Az
    I think on a 10 ton unit I'd follow the above recommendations. Verify no leaks (500 micron vac and hold) and stay with R-22.
    Jim
    Tucson, Az
    Keeping the Ice Cream Frozen!
    Apr 2013
    Thx for the input. Think I'll stay with 22
    Jun 2013
    The Hot South
    Flush with R11 huh?
    daledehart19
    Quote Originally Posted by jtrammel View Post
    I have seen that you use R421A in a couple of other threads I have seen. Just wondering what kind of results you are seeing, and if you are noticing any real capacity loss or any unexpected draw backs or benefits. I just retrofitted one to R421A today, so I haven't gotten to see any long term results.