    I'm seeing superheat around 60 and subcool around 18. This is a 4 ton water-air unit, and according to my unit's charts the high side pressure is low in all modes but especially during heating. Am I looking at low charge or bad TXV or both?
    Jul 2009
    Columbia, MD
    could be a measurement error. try adjusting the txv valve counter clockwise to decrease your superheat, then recheck both SC and SH
    May 2009
    central ohio
    what freeon is it it does sound like txv issue but u will need to make sure that heat transfer in evap is ok or the reading u r taking will not b accurate