    40 degree outside air, need to turn chiller on

    Just started new job 2 months ago,,worked in residential for 10 years,this is my first industrial/commercial job..All greek to me,but im learning a lot everyday.Dont understand one thing though,why the hell do i need to turn the chiller on when its 40 degrees outside...Always thought economizers were invented to give free ac when needed...if i dont turn off the 5 million btu boiler when its 40 and turn on the chiller,,the building gets in the lower 80's,just doesnt seem right to turn on the ac at 40....its been like this ever since it was installed,my guess is low-bid install...any feedback?

  2. #2
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    with 40F OA you should be mixing that with RA and dumping some of the same return,the space sounds like it has a good interior load once the day gets going with people and lighting loads ETC.if your AHUs are setup for econo the coils should be drained of the chilled water for the winter,and your AHUs should be setpoint controlled on the heating coils from DA or even RA...are there heating coils in the same chilled water AHUs.
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    welcome to commercial/industrial world! mother nature still works the same in this world as it did in the resi world...mistakes just cost more and make bigger bangs we also have a lot of dumb installers, techs and engineers in this world...and some great ones too. keeping that in mind, you may be correct...someone may have messed up...investigate it. at the very least, you will learn something and the customer will be greatful that you check out everything.

    you may have an interior space that needs cooling year round. you may have a space that has humidity concerns. if you can not get the proper amount of air to the space with the correct air properties, you may have to mechanically condition it.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  4. #4
    Join Date
    Jan 2003
    Location
    San Jose, Ca
    Posts
    2,089
    Post Likes
    If your building is just office space and you have an operating eccon system you should not need mechanical cooling.

    If you have data centers of process areas then they may dictate other operations.
    Old snipes don't die they just loose their steam

  5. #5
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Post Likes
    Quote Originally Posted by krptonicx View Post
    Just started new job 2 months ago,,worked in residential for 10 years,this is my first industrial/commercial job..All greek to me,but im learning a lot everyday.Dont understand one thing though,why the hell do i need to turn the chiller on when its 40 degrees outside...Always thought economizers were invented to give free ac when needed...if i dont turn off the 5 million btu boiler when its 40 and turn on the chiller,,the building gets in the lower 80's,just doesnt seem right to turn on the ac at 40....its been like this ever since it was installed,my guess is low-bid install...any feedback?
    What are your mixed air dampers doing on your air handlers? Is your economizer working? What's your discharge air set point? What is your discharge air temp with economizer running? Your dampers are not modulating to mix outside air so you have to run the chiller. That would be my first approach.

  6. #6
    Join Date
    Jan 2004
    Location
    Oregon
    Posts
    2,096
    Post Likes
    Put it this way, if the mechnical engineer was experienced, good and not just out of school you should not need a chiller at 40 deg.Problem is there is alot of lousy engineers out there and that is where we come in, to fix there problems.I have walked on lots of jobs and heard, your controls suck, your AHU's can't keep up , yada, yada yada, and I always say, the best equipment in the world can't fix the worst engineereing in the world, simple as that.

  7. #7
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    Quote Originally Posted by acjourneyman View Post
    Put it this way, if the mechnical engineer was experienced, good and not just out of school you should not need a chiller at 40 deg.Problem is there is alot of lousy engineers out there and that is where we come in, to fix there problems.I have walked on lots of jobs and heard, your controls suck, your AHU's can't keep up , yada, yada yada, and I always say, the best equipment in the world can't fix the worst engineereing in the world, simple as that.
    very well written journeyman!



    .

  8. #8
    Join Date
    Jan 2003
    Location
    San Jose, Ca
    Posts
    2,089
    Post Likes
    Quote Originally Posted by acjourneyman View Post
    Put it this way, if the mechnical engineer was experienced, good and not just out of school you should not need a chiller at 40 deg.Problem is there is alot of lousy engineers out there and that is where we come in, to fix there problems.I have walked on lots of jobs and heard, your controls suck, your AHU's can't keep up , yada, yada yada, and I always say, the best equipment in the world can't fix the worst engineereing in the world, simple as that.

    Boy ain't that the truth
    Old snipes don't die they just loose their steam

  9. #9
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes

    Question

    Quote Originally Posted by krptonicx View Post
    ..... this is my first industrial/commercial job.

    ... , why the hell do i need to turn the chiller on when its 40 degrees outside. economizers were invented to give free ac when needed.

    its been like this ever since it was installed, my guess is low-bid install.

    any feedback?
    What type of industry?
    What are the internal gains?

    Is an economizer currently installed?
    If not, is it reasonable to plan an upgrade and retrofit the unit to reduce the ever increasing operating costs?

    If yes, How is the economizer set-up?

    Like big johnson states
    Your dampers are not modulating to mix outside air so you have to run the chiller.

    Fix might be relatively simple, if someone knows the current control scheme.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  10. #10
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    1,024
    Post Likes
    do you have a water side economizer for the chilled side ? you will have a large plate heat exchanger and valves in pipe to bypass chiller and cool water using the cooling tower

  11. #11
    Join Date
    Dec 2006
    Location
    Oz
    Posts
    150
    Post Likes
    You are probably right about the low-bid... but it doesn't go back to the installer as he's usually just installing as per engineering plans. You can't really drop it in the lap of the engineers either as they have been given a budget to stay within. It goes back to the bean-counters who get a pat on the head and a huge bonus from the big boss when the project comes in at $500K under projection. Everyone forgets to tell the boss that he's going to lose his shirt on inefficiencies by running chillers at 40.

    Contractors report to engineers
    Engineers report to planners
    Planners report to bean-counters
    Bean-counters kneel under the bosses desk and work to please...

    Once again, if the boss would just talk to the engineers, he'd be clued in, but because he can't be bothered, he pays in the end as everyone's had a dash for savin' cash in between.

    IMO the only people who aren't influenced are the engineers and contractors. It's to their benefit to make a larger, more complicated install as they get paid more.

    I just commissioned a multi-chiller install that assuredly cost millions yet didn't have a single air-purge valve on any chilled water line. Why? Because they cost too much money and they will be added as a "variation" later if they absolutely have to have them.

    Tell me where that came from?

  12. #12
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Post Likes
    It appears that krptonicx has left the building leaving the rest to rant and rave about design engineers.

  13. #13
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes
    Quote Originally Posted by tex~n~oz View Post
    IMO the only people who aren't influenced are the engineers and contractors.

    It's to their benefit to make a larger, more complicated install as they get paid more. << ... Tell me where that came from?
    Original design engineering is based on a fixed fee.

    Of course, it may be quite different in the land of OZ
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  14. #14
    Join Date
    Sep 2004
    Location
    crossville
    Posts
    624
    Post Likes

    Red face yes but

    Quote Originally Posted by dan sw fl View Post
    Original design engineering is based on a fixed fee.

    Of course, it may be quite different in the land of OZ
    it can also be cut during build, and many things could have been left out. ran into this in an new city hall being built, they cut out controls, water by pass valves, and improper water flow thru chillers, resulted in fllod back and took out all the compressors, 400 tons worth.in less than 14 months of ops
    If you cant cool it
    HEAT THE Hello out of it

  15. #15
    Join Date
    Dec 2006
    Location
    Oz
    Posts
    150
    Post Likes
    It's my understanding that the engineering firm charges a commission based on winning bid, not to include any later variations, on top of a previously agreed upon fee.

    That's my understanding and it would make sense.

    The more complicated the system, the more liability on the engineering firm, the more man hours to design, the more money they get on the bottom line.

  16. #16
    Join Date
    Jan 2007
    Posts
    4
    Post Likes
    Thread Starter
    basically,from what i can gather,its just a low bid installation..Its state of ct office buildings..I am gunna have one helluva time doing any repairs on these unites,they are literally shoehorned in above the drop ceiling.I changed the filters on the 67 fan coils in one building,and literally had to fold up the filters like accordians to get them in there...Never seen anything like it.

  17. #17
    Join Date
    Feb 2007
    Posts
    39
    Post Likes

    Chiller

    Does the chiller short cycle

  18. #18
    Join Date
    Mar 2005
    Location
    Mountain/Pacific Time Zone Typicallly
    Posts
    4,592
    Post Likes
    We have a system that we have to run the same way. Fan coils with heating and cooling on each floor and the only outside air available is the minimum outside air intake required for each floor. Sun comes up and its around 40 degrees OAT, the solar load is enough that we have to bring on the chiller. No water side economizer either.
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    My 5 yr old son "Dad, Siri is not very smart when there's no internet."


  19. #19
    Join Date
    Dec 2006
    Location
    Oz
    Posts
    150
    Post Likes
    Quote Originally Posted by krptonicx View Post
    basically,from what i can gather,its just a low bid installation..Its state of ct office buildings..I am gunna have one helluva time doing any repairs on these unites,they are literally shoehorned in above the drop ceiling.I changed the filters on the 67 fan coils in one building,and literally had to fold up the filters like accordians to get them in there...Never seen anything like it.
    When I was in service, I had a building with almost the same set-up. Water-source heat pumps just stuck anywhere they could find a place to stab em. Of the 150 units, there were about half a dozen that never did get a filter change as they couldn't be gotten to without dropping the whole unit.
    Sounds like they've done the same thing with your fan coils...

    It took years, but I finally found out why.... Cheap as hell to buy, install and duct with flex. The engineers didn't care if you couldn't get to the filters.. Not their problem and by the time it was a real issue, the job was signed off and paid for.
    It costs just a fraction to put these types of systems in place as compaired to a properly designed system with central AHUs, VAVs and metal ducting, economizers, etc.

    Don't shoot the installers, it was the bean-counters behind the smoking gun on this one. They wanted CHEAP and you got it.

    Be thankful for small blessings though.. No compressors or reversing valves to change out while balanced over someone's desk; while you're holding a hot torch in a small dusty cabinet with a mirror in your teeth to see what you're doing.

    I had almost forgotten about that miserable migraine of a place....... It was a mental hospital and more times than not, I just wanted a room at the end of the day.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •