    Liebert

    M\N-MMD18E-PHEOP,S\N-992000106057
    today was the first time ever having to work on one ,the humidifier is not working and it's going into alarm,water fill valve works and goes through the cannister & out the drain,cannister was not hot,removed wire from fill valve and water shuts off,the book for the unit was not there so i'm not really sure what is wrong,thanks for any suggestions

  2. #2
    Join Date
    Mar 2007
    Location
    FL
    Posts
    29
    What was your alarm display on your operating controller? Your cannister may be max usage, did the contactor pull in for the electrodes? If you filled it and it drained w/o the contactor pulling in can has reached max.Go to lieb ert.com for IOM's.

  3. #3
    Join Date
    Sep 2004
    Location
    crossville
    Posts
    606

    Thumbs up two things

    depending on the style,
    some are true electrolisis steam generated, meaning they pass current thru the water, and if the water is CLEAN, meaning there isnt enough conductivity it wont steam, this usually occurs after and dump and fill cycle, I have had to add salt to the water to get one to start steaming, second if the heat element rods have depeleted then its time to replace the steam generator canistor.
    If you cant cool it
    HEAT THE Hello out of it

  4. #4
    Join Date
    Oct 2005
    Location
    Ohio
    Posts
    41
    the alarm said humidifier problem,setpoint is 30%,low humidity setpoint is 15%,the controller stated 17% room humidity and it was in the humidify mode but the cannister was cold

  5. #5
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by rix870 View Post
    the alarm said humidifier problem,setpoint is 30%,low humidity setpoint is 15%,the controller stated 17% room humidity and it was in the humidify mode but the cannister was cold

    holy bajibers that humidity setting is way to low (if there are computers present)



    .

  6. #6
    Join Date
    Dec 2004
    Location
    newton,mass.
    Posts
    6,109
    Check the run/drain switch. The canister will not be hot if water is not staying in it.
    "Nothing else can poison our culture, corrupt our society or ruin the character of our people like unearned money or unearned opportunity." -- James R. Cook

    "Fooling around with alternating current is just a waste of time. Nobody will use it, ever." Thomas Edison, 1889.

  7. #7
    Join Date
    Aug 2006
    Posts
    177
    limit switch under the pan

  8. #8
    Join Date
    Aug 2006
    Posts
    177
    oops wrong model

  9. #9
    Join Date
    Aug 2006
    Posts
    177
    is there a float switch

  10. #10
    Join Date
    Aug 2006
    Posts
    442
    yes

  11. #11
    Join Date
    Feb 2007
    Posts
    533
    Posting the Model number makes it possible to help. You have a 1 1/2 ton MiniMate With a steam generator Humidifier.

    Here is your link to the manual... Section 6.3.1 deals with the humidifier...

    Good luck

    http://www.liebert.com/assets/produc...t/sl_10530.pdf

  12. #12
    Join Date
    Aug 2006
    Location
    Wisconsin
    Posts
    1,504
    If the fill valve is open but the cylinder dosen't fill, the drain valve probably has crap in it. Clean the drain valve.
    Buy American! The job you save may be your own.

  13. #13
    Join Date
    Sep 2004
    Location
    crossville
    Posts
    606

    Thumbs up like i said

    Quote Originally Posted by esornivram View Post
    depending on the style,
    some are true electrolisis steam generated, meaning they pass current thru the water, and if the water is CLEAN, meaning there isnt enough conductivity it wont steam, this usually occurs after and dump and fill cycle, I have had to add salt to the water to get one to start steaming, second if the heat element rods have depeleted then its time to replace the steam generator canistor.
    read 6.3.2 add small amount of salt to water and see if it goes to steaming
    if it does then have the water checked for the incoming conductivity levels
    some city water is so clean it wont steam, the conducitivy level should be above 200
    I added an swimming pool chlorinator to one once so it would keep working for an extended time frame, the city water was below 60 and wouldnt pass the current of the steam generator
    Last edited by esornivram; 03-08-2007 at 12:20 AM.
    If you cant cool it
    HEAT THE Hello out of it

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event