With my new company I'm starting to do a lot of cool things I never was able to do before and starting to run into a few issues. I'm working for a Schneider I/A rep now and have a job with a Jace, 5 MNL controllers and 3 Trane CSCs with LCI-I cards in them. I can discover all controllers. I can discover all points. I can see the values changing on the MNLs but I'm getting no info from the LCI-Is(points reading 0, nan, etc.). I changed the subnet and node numbers to be on the same subnet as the MNLs and the nodes are in numerical order behind the MNLs, and guidance or ideas are appreciated.