    Issues with HPC

    I have been working on a good friend of mines 3 year old Armstrong heat pump the past couple of evenings and boy has it been a good one. The first day i showed up and found the compressor had shorted out causing a funky burnout, i go to the supply house the next day and pick up the warranty compressor and get it installed. Purged the lines, installed a new bi-flow liquid line drier, triple evacuated the system and dumped the factory recommended 410a charge into the system. Fired the compressor up and got equal pressures on the discharge and suction lines. Reversing valve was bad, come back the next day and put the dreaded reversing valve in the was also under warranty, triple evacuated, charged it back up. Fired the system up again everything is running good in cooling, adjusted the charge to 15* subcooling, 12* superheat, everything is looking good. Started packing my tools up in the truck and i told by buddy i wanted to check heat mode, compressor fired up and kicked out on high pressure within 10 seconds. I know i have a blockage in the system somewhere and i am pretty sure it is the condensing unit TXV, its the only thing that makes sense to me. I just wanted to run it by you guys to make sure i am not missing anything so i do not have to break the bad news to my buddy for the 4th time. Thanks in advance.

  2. #2
    Join Date
    Jun 2007
    Location
    Greenwood Indiana (Indianapolis)
    Posts
    420
    So you weighted in the factory charge. Great. Then you say you adjusted it to superheat and sub-cool. Is the indoor metering device a txv? When I hear "adjusted the charge" to me that means you added charge. You could be over charged. Or you don't have good indoor air flow. 15 Subcool is a little high. Is the indoor unit properly matched? When I am working on a heat pump, I turn it on in the A/C mode, then when I need to check it in heat, I disconnect the orange wire only. If this is dual fuel, maybe the gas furnace was on?

    It very well could be the txv. Usually the low side pumps down when this happens.
    As iron sharpens iron so one man sharpens another Proverbs 27:17 NIV84

  3. #3
    Join Date
    May 2011
    Location
    Southwest VA
    Posts
    21
    The evaporator has a non adjustable TXV on it, the condenser and evaporator coils are clean, 15* sub cooling is the factory recommendation. I doubt there are airflow issues since the system was running perfectly in cooling. I am curious as to what else can cause a blockage in a heat pump system in heat mode and not in cool.

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    19,532
    Quote Originally Posted by jdbradley View Post
    The evaporator has a non adjustable TXV on it, the condenser and evaporator coils are clean, 15* sub cooling is the factory recommendation. I doubt there are airflow issues since the system was running perfectly in cooling. I am curious as to what else can cause a blockage in a heat pump system in heat mode and not in cool.
    Heat mode? How about the outdoor metering device?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  5. #5
    Join Date
    May 2011
    Location
    Southwest VA
    Posts
    21
    That is what i am thinking, i was just curious if anyone else has run into this issue. I have never had a burnout create this much havoc in a heat pump before.

  6. #6
    Join Date
    Dec 2006
    Location
    new england
    Posts
    651
    Is the condenser a micro-channel?
    Chaos equals cash$$$

  7. #7
    Join Date
    Dec 2006
    Location
    new england
    Posts
    651
    What's the make and model of the unit.
    Chaos equals cash$$$

  8. #8
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    310
    Is this a matched system and the air handler installed at the same time as the heat pump? If not I bet its overcharged even if you weighed it in by the nameplate.

  9. #9
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,762
    Sounds like overcharged to me, maybe low id airflow too.

  10. #10
    Join Date
    Feb 2013
    Location
    Nashville, TN
    Posts
    20
    all your txv's job to do is maintain superheat somewhere between 8-15 As long as it has saturated liquid coming into it. It sounds like your txv is doing its job. Check airflow.

  11. #11
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,256
    I've seen units charged to 12-15* subcool trip in heat mode on high pressure. If indoor temp is at the normal levels of comfort I'll only go up to 8*, unless other factors like long line set or vertical pressure loss are issues.

    Get a subcool measurement in heat mode, see what it does before it trips.

  12. #12
    Join Date
    May 2011
    Location
    Southwest VA
    Posts
    21
    Thanks for the replies. It does not have micro channel coils, it is a matching Armstrong setup, the condensing unit is an Armstrong 4SHP13LE136P-1 serial is 1609F00406. I checked the evaporator coil which was in pretty good shape, put a new filter in it. The reason i was leaning towards the external TXV is, this unit is equipped with the TXV's with internal bypass. An overcharge does make sense, the data plate says the factory charge is 10lbs 2 oz which does seem a little high for a 3 ton unit with about 15' of line set. I will pull some of the charge out and bring it down to 5 degrees or so of subcooling and see if it will run in heat before i change out the expansion valve. Thanks for the help, this is a great site!

  13. #13
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,256
    Let us know how it turns out.

    Get your post count over 15 and apply for pro membership, one of the best things you can do to be a better tech is get into the locked pro forum.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event