    Quote Originally Posted by philjafo View Post
    Better, but you've still got a power vented furnace and a naturally vented water heater sharing a flue.
    Who doesnt? Its still venting at negative pressure.
    May 2013
    STP, MN
    So why didn't the H/O have you do #'s 2-5?
    In a boiler room
    Quote Originally Posted by JKopp View Post
    We learned that securing only the top of w/h allowed them to walk so code dictates two straps now.
    Fau has inducer fan for combustion gases not power vented, this combo venting is allowed.
    It is allowed but not safe.
    NE wisconsin
    If the vent becomes blocked, the furnace can force exhaust out of the vent hood for the water heater. As chuck said its allowed but not safe.
    Dec 2012
    columbus, OH
    Huh:? 99% of homes around here are vented in this fashion
    Dec 2012
    columbus, OH
    Five things wrong with this water heater install
    Makes sense if the pressure switch is bypassed as well.
    In a boiler room
    Quote Originally Posted by Core_d View Post
    If the flue gets restricted or plugged the furnace will vent out the water heater draft hood, there is no safety to shut it down.
    It's the most dangerous code approved installation. And if someone gets CO poisoned it won't matter if you followed the code. The installer has final responsibility for safe operation.
    Aug 2008
    San Clemente, CA
    Our area requires fau to breath outside air and in this case the w/h too. The w/h vent was spilling regardless of the fau combo vent as it was not vented correctly. I will let the plumber fix his issues as I am not a licensed plumber, only a C20 licensed HVAC contractor.