    Exclamation fan running

    I have new rudd mod ubhk-24j185fa unit with heat pump and the fan will not shut off in heat mode. The installer has put a differant honeywell therostat on and it still stays on.I pulled the therostat from the wiring and it still runs .I HAVE TO TURN THE BREAKER OFF.iT WORKS FINE IN COOL MODE. Rudd tells him its the thermostat and to set it up like its a gas unit the therostat does not have that opt when you choose heat pump. Can anyone help.

  2. #2
    Join Date
    Mar 2007
    Location
    INMAN,SC
    Posts
    1
    Post Likes

    Hmm

    could be a bad heat sequencer.

  3. #3
    Join Date
    Jan 2007
    Posts
    328
    Post Likes
    Are you saying that when stat is put into heat mode the fan will start eventhough the temp setpoint is satisfied?
    Or are you saying once heating cycle is over the fan just won't shut off?
    If it is the first question then, your stat may be screwed up or not set-up right.
    If it is the second question then, you could have a fan control problem.
    The option for turning the fan on as soon as a call for heat is initiated is by programming for a heat pump. Programming for gas heat will allow fan to start with furnace's control board timer. If you have dual fuel (gas heat w/heatpump)then you need to program it for dual fuel by getting yourself the right stat. Are you using Emergency heat when this occurs? If so, then your stat is the wrong type or it is not configured properly.
    Believe none of what you hear and half of what you see.

  4. #4
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    If the installer isn't YOU, call him back, his work must be guarenteed.
    If everything was always done "by the book"....the book would never change.

  5. #5
    Join Date
    May 2003
    Location
    Dixie
    Posts
    1,352
    Post Likes
    If the installer put on a new t-stat and didn't check operation of your unit then you need to call his service manager, unless they were ...err...hacks....cough cough
    It is time for all good men to come to the aid of their country, for we are in deep crap.

  6. #6
    Join Date
    Jun 2001
    Location
    Greater Philadelphia Area
    Posts
    124
    Post Likes
    What model stat? Air handler does have field selectable interface dip switches... is it possible there is a continuous fan option activated on the board? If installers manual is with the equipment, dip switch info can be found there. Qualified tech can troubleshoot a fan issue quickly.

  7. #7
    Join Date
    Mar 2007
    Posts
    2
    Post Likes
    Thread Starter

    fan control

    Quote Originally Posted by iwannahelp View Post
    Are you saying that when stat is put into heat mode the fan will start eventhough the temp setpoint is satisfied?
    Or are you saying once heating cycle is over the fan just won't shut off?
    If it is the first question then, your stat may be screwed up or not set-up right.
    If it is the second question then, you could have a fan control problem.
    The option for turning the fan on as soon as a call for heat is initiated is by programming for a heat pump. Programming for gas heat will allow fan to start with furnace's control board timer. If you have dual fuel (gas heat w/heatpump)then you need to program it for dual fuel by getting yourself the right stat. Are you using Emergency heat when this occurs? If so, then your stat is the wrong type or it is not configured properly.
    Yes to both questons,this is the secound honeywell 8000 series stat.IT has only one choice for heat pump with aux heat.The does shut off after 5 min if you remove the stat.

  8. #8
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    If you pulled the stat off the wall away from the wiring, and the fan still runs, it's not the Stat. Call the company's owner and ask to send a real tech out.
    If everything was always done "by the book"....the book would never change.

  9. #9
    Join Date
    Jan 2007
    Location
    Western Suburbs of Philly
    Posts
    430
    Post Likes
    a good tech should be able to nail this down fairly easily

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •