    Quote Originally Posted by gem6376 View Post
    That is not why it is short cycling.
    You asked a couple posts above if that can be the cause of the short cycling.

  2. #15
    Join Date
    Nov 2009
    Location
    Oakland County Mi
    Posts
    24
    I asked if it could be the result.

  3. #16
    Quote Originally Posted by gem6376 View Post
    Anyone know if this leak pictured is field repairable.

    Attachment 385161
    its definitely repairable like previously said, its just an oring. get the service bulletin, dont remember off hand which one, and be careful when splitting housing or you will be replacing compressor.

  4. #17
    Join Date
    Dec 2008
    Posts
    112
    Quote Originally Posted by traneguy123 View Post
    its definitely repairable like previously said, its just an oring. get the service bulletin, dont remember off hand which one, and be careful when splitting housing or you will be replacing compressor.
    Thank you. I was able to get out of the rain today, obtained the literature I need. Pretty straight forward.

  5. #18
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,081

  6. #19
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,075
    I've done em. Even made a video.
    It might get loud!

  7. #20
    Join Date
    Dec 2008
    Posts
    112
    This was completed, and another since. Takes about 5 hours, one man, minimal material and about as complicated as replacing a condenser fan motor.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event