Network 8000 software
What software is required to make changes to Network 8000 controllres
eg.MZ2-1 controllers
-
03-01-2007, 10:14 AM #2
If you are talking about the old Barber Colmans - PSI
-
03-01-2007, 10:29 AM #3
Waiting Email Confirmation
- Join Date
- Jan 2006
- Posts
- 16
Correct it is the old Barber Coleman. Price book lists two part numbers
LAPT-80800-EPSI
LAPT-80800-PSI
-
03-01-2007, 10:36 AM #4
I have them - do you need them?
-
03-01-2007, 10:40 AM #5
What is the difference between EPSI and PSI?
I have one of them, will have to check which one.
kontrol out"Can't we all just get a Lon?" - Garry Jack
"BACnet: integration or interrogation?" - The Janitor
"Open protocols? You can't handle open protocols!" - Nathan R. Jessup
“What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
-
03-01-2007, 10:47 AM #6
Can't remember, Haven't used them in a while. However the 3 1/2" thick manual might tell me!
-
03-01-2007, 01:44 PM #7
motec, I can send you those files if you need them. My email address is in my profile. My distributer gave them to me free because he laughed when I told them I had several buidings with them. He couldn't believe they were still being used. It always amazes me how long some of our stuff holds up (or not).
Last edited by HVAC Teacher; 03-01-2007 at 01:45 PM. Reason: unwanted urls automatically added
-
03-01-2007, 03:21 PM #8
Regular Guest
- Join Date
- Jul 2001
- Location
- Canada
- Posts
- 1,710
Lots of NETWORK 8000 still working away , first NW8000 controllers I put in back in 1986 are still running today. EPSI-1 is the extended version of PSI
-
03-02-2007, 08:58 PM #9
Regular Guest
- Join Date
- Feb 2007
- Location
- Sacramento, CA
- Posts
- 52
What are you changing? The programming in the GCM/LCM's or in the ASD devices. You can use Hyperterminal to get into a GCM or LCM & modify it's programming. You really only need PSI if you are going to modify the programming in Microzones, PEM's or Microflo's.
-
03-05-2007, 05:38 AM #10
Waiting Email Confirmation
- Join Date
- Jan 2006
- Posts
- 16
Thanks for the reply. Yes to all, as I may have to modify the asd controls.
When connecting to the GCM or LCM with hyper terminal are you connecting
to the the 25 pin connection as a direct connect?
-
03-07-2007, 12:16 AM #11
Regular Guest
- Join Date
- Feb 2007
- Location
- Sacramento, CA
- Posts
- 52
Yes, connect to the 25 pin connection. You may have to change the port switch for connection setting, it depends on your cable.
-
06-04-2007, 05:25 PM #12
Regular Guest
- Join Date
- Feb 2007
- Posts
- 1
Recently had a system 8000 dumped in my lap. Can't see a thing and very little is working. The rep left an Atari Portfolio with the interface and no more.
There is no chance they will show up to check the system out, but they will upgrade (of course !!).System has Microzone II controllers bussed together. Help!!!!
-
06-05-2007, 08:31 AM #13
Regular Guest
- Join Date
- Jul 2001
- Location
- Canada
- Posts
- 1,710
The ATARI's worked fairly well to access the NETWORK 8000 systems , BARBER COLMAN did not promote them very long, I think I still have the manual on it around here someplace.