02-27-2007, 01:56 PM #1
slow ice
trying to get 6-8 degress of superheat on a scotsman flaker, cleaned condensor, charged to 225psig and which subsequently got me to 32psig suction, has 14 degree superheat.
factory book said it should be @ 30psig suction, factory tech support said i should have 225 - 250 psig discharge.
any advice? its a pet project and I havent really seen any refrigeration since school.Anything worth doing, is worth doing right......the first time!!!
-
02-27-2007, 05:14 PM #2
did you charge this unit with a scale? critical charge in unit, and charging to a recommended head pressure is not the way to do it. although you cleaned the condenser, it may still be somewhat dirty, and using head pressure to determine charge should be avoided. is this machine self contained, or does it have a remote condenser?
-
02-27-2007, 06:40 PM #3
Just to add
What machine?
What Model & Serial #?
What Refrigerant?
Charging by head pressure. Thats a new one.
-
02-27-2007, 06:51 PM #4
Ranken grad eh?
Flakers can be quite unforgiving. As others have stated, weighing in the proper charge is VERY important.
Do not play with the TEV or your gonna regret it.
Since you did not say what gas you got in it, no one knows what your SCT is so they can not be of much assistance.
-
02-27-2007, 07:11 PM #5
weigh it in
weight it in
weigh it in
and by the way....
weigh it in
It is time for all good men to come to the aid of their country, for we are in deep crap.
-
02-27-2007, 09:00 PM #6
Professional Member
- Join Date
- Aug 2006
- Posts
- 442
Weighing the charge in on Ice machine is absolute must
-
02-27-2007, 09:35 PM #7
Yes, I went to Ranken.
Unit is 502, model is r800....Anything worth doing, is worth doing right......the first time!!!
-
02-27-2007, 10:23 PM #8
In case no one else mentioned it:
Weigh in the charge
And use itty bitty short hoses
And listen to idontgetit. you WILL be sorry if you mess with TEV if you are not absolutely sure it is the problem.
-
02-27-2007, 11:03 PM #9
Kewl, it was not meant to be offensive.
You put 502 back in it or 408?
How is the float level? High water level = high superheat on a flaker.
If it was 408, my experiences indicate that the 80% or 85% of wieght rules need to be flexed on some machines and you really just have to tweak them a bit.
Get er all very very clean, lower the float level below normal, perhaps 1" in the bottom of the bowl, check the superheat, if high, check subcooling, add gas till 10 degrees subcool, check superheat if not right, add more gas monitoring subcool so as to never exceede 15 subcool or RLA of comp, check superheat--- it will be on the spot.
You can confirm superheat/TEV operation by warming the bulb after you get the 10 subcooling, before that your gonna be lookin at glide problems that can give unexpected results.
Anymore questions on it?
-
02-27-2007, 11:25 PM #10
I didnt take it offensive, I was taken back by the Q?, wasnt expecting it.
Ill have some time on it tomorrow.
Thanks to all for the input.Anything worth doing, is worth doing right......the first time!!!
-
02-28-2007, 09:40 PM #11
Well got in and it looks to be working, had almost empty bin when I left and noe ive got more than 300lbs.
Anything worth doing, is worth doing right......the first time!!!
-
02-28-2007, 10:19 PM #12
Good deal. Love them icemakers myself!
-
02-28-2007, 10:24 PM #13
especially when they're free. it will be really handy this summer
Anything worth doing, is worth doing right......the first time!!!