    Quote Originally Posted by beenthere View Post
    If the IAQ is wired up correctly, and set up correctly, it will slow the blower during normal cooling calls if the RH is above set point.
    Yea this is the other problem. The wiring is not set up properly causing the blower not to go down to 70% cfm if RH is above set point. The main issue is the blower runs at 100% cfm instead of slowly ramping up like it should since the dipswitches are set to that position.

  2. #41
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    We had a tech come in today to replace the first section of the main trunk with metal. Airflow does seem slightly more, but the tech said the kink in the old duct wasn't that bad.

    He looked at the wiring on the IAQ and said he doesn't know what is wrong. I told him all I wanted was the ramping profile fixed on the blower. He made sure the dipswitches were set properly and they are. The blower is still only running at 100% cfm. I want the system to be operating the way it used to be before the on-board link was cut for the humidity feature. It used to run around 1060 cfm for 7 1/2 minutes, then go to 1220 cfm for the rest of the cycle. The tech can't figure why the blower won't ramp up anymore. Any further ideas??

  3. #42
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,511
    Post Likes
    Not sure it can once the link/jumper is cut.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #43
    Join Date
    Sep 2012
    Posts
    373
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    Not sure it can once the link/jumper is cut.
    Thanks. We had another tech from the installing company come yesterday and said the speed only ramps to 100% because the on board link (R to DS) was cut. He jumpered those back together and still didn't work. However, the decreased blower speed slightly to help with dehumidification and the system is dehumidifying better than before. The only way that the ramping could work again is if the control board was replaced. So basically I'm satisfied with everything for now and I'll post back if I have any further questions! Thanks again!