Quote Originally Posted by beenthere View Post
If the IAQ is wired up correctly, and set up correctly, it will slow the blower during normal cooling calls if the RH is above set point.
Yea this is the other problem. The wiring is not set up properly causing the blower not to go down to 70% cfm if RH is above set point. The main issue is the blower runs at 100% cfm instead of slowly ramping up like it should since the dipswitches are set to that position.