    Hmm zone dampering

    Does anyone have any experience in zone dampering systems on big rooftop units. I understand there are types available with adjustable static settings depending on your desires. I have a rather large rooftop with only 2 major ducts I want to put automatic dampers in

  2. #2
    Join Date
    Mar 2005
    Location
    Pacific Time Zone
    Posts
    4,195
    Why do you want to put automatic dampers in these two zones? Temperature control, different schedules for different zones, other?
    Do you have a vfd or inlet vanes on this RTU's supply fan? Is there more than one fan, supply, return and exhaust/relief?
    If you put in zone dampers and you do not have a vfd or vanes you will need to add a vfd and a static pressure transducer or add a bypass damper with a static pressure transducer. Is this a DX system and does the unit have heat and if it does what type? You need to be careful and take various measures if this is a large RTU when adding zone dampers as you could over pressurize the duct work and blow it apart. I would recommend contacting a local HVAC company that does commercial controls to assist you with what you are wanting to do.
    "How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
    BIG Government = More Dependents
    "Any 'standard' would be great if it didn't get bastardised by corporate self interest." MatrixTransform
    http://threedevilskennel.com/ - not my website.
    Versatile Hunting Dog Federation - www.vhdf.org/


  3. #3
    Join Date
    Dec 2006
    Location
    Washington, DC
    Posts
    506
    /agree with Crab, contact someone who installs these.

    Going with a zoning system like Tranes VariTrac or Carrier's 3V is to your benefit. The systems have alot of settings in the programming to protect the equipment & duct.

  4. #4
    Join Date
    Aug 2006
    Location
    NY
    Posts
    230
    Quote Originally Posted by mechanaman View Post
    Does anyone have any experience in zone dampering systems on big rooftop units. I understand there are types available with adjustable static settings depending on your desires. I have a rather large rooftop with only 2 major ducts I want to put automatic dampers in
    Mechanaman,

    Can you be more specific in regards to the application. Tonnage, load, sq/ft of the 2 zones to be, the size of the 2 ducts, ....plenum ceiling?

    Why do you wish to split the load. Is it a landlord thing, splitting suites, or temperatures uneven? Averaging controls can rectify some issues.

    I have quite a few years experience in zoning retrofits, as well as new VAV design/build. I may be able to give some simple input with a little more data.
    Thank you for reading, and have a nice day

  5. #5
    Join Date
    Mar 2007
    Location
    Midwest
    Posts
    19

    Carrier 3V

    Here is a link for the Carrier 3V product databook which you will find helpful.

    The new Carrier 3V is pretty slick and easy to setup.

    There is also a demo on the Carrier website which runs through the whole setup.

    http://www.xpedio.carrier.com/idc/gr...t/33zc-1pd.pdf