    Over amperage on cook return fan
    Ive got a 1.5 hp 1750 rpm 460 volt return fan motor that has been giving me issues overamping for the last 2 months. The freq drive is tripping on calculated motor temp. Basically it monitors the motors amperage and bases that on motor temperature. The nameplate states that at 460 volt the motor should pull 2.2 amps. The motor is pulling 3 to 3.5 amps. I replaced it with a weg motor with the same nameplate data. New motor is doing the same thing. Ive checked all my connections, looked at the contacts on the contactor. Everything looks good. I even bypassed the drive itself by running temporary wires directly from the disconnect to the motor. Same problem. The fan spins freely, as free as the identical one located in the same mech room which is running normal at 1.8 amps. The belt is snug like it should be. Remove the belt and the motor pulls .8 amps. My voltage looks good at 492 across all three legs. Something has changed in the last 2 months that is now causing this problem. Any ideas?
    Southeastern Pa
    I'm not sure about what a "weg" motor is.
    Are we talking single phase?
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Mar 2013
    Va
    3 phase. Weg is the motor manufacturer. http://www.weg.net/us. Hopefully links are allowed.
    Southeastern Pa
    Are current readings being taken at the VFD or at the motor?
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Mar 2013
    Va
    At disconnect, drive, and motor.
    Southern,Ca
    is there a restriction in the ductwork? is this a grease hood are there grease filters that are plugged up
    Dec 2003
    The fan is moving more air if its pulling more amps. What could have changed to put less resistance on the fan and let it move more air? Thats what you need to be thinking about. Cant you do something in the drive to limit the speed to keep it from tripping?
    Southern,Ca
    Quote Originally Posted by bigtime View Post
    Good point. With that said it is possible that an access door has either fallen off or been left off by the grease guys. That is if it is a grease hood
    Sent from my SCH-I535 using Tapatalk 2
    Jun 2012
    East tx
    Adjustable pulleys?
    Southern,Ca
    Quote Originally Posted by Crazecodyk View Post
    Adjustable pulleys?
    Most of the vfd exhausts I've seen are direct drive but I guess we will have to wait until he answeres
    Southern,Ca
    Another possibility is that they changed the grease filters to a less restrictive style and that vfd was set spot on for the amperage than the filters were changed and it was now overamping! But again that is only if there are filters
    Mar 2013
    Va
    This is a return fan not an exhaust fan. There werent any access doors or anything of the like i can find left open. This problem started about 2 months ago. I also have 3 other ex fans on the roof pulling higher then normal amps. Ive had the power company check there incoming power from there transformer. They say everything looks good on there end? The only maintenance that was done now that i think about it was a filter change. Prefilters and Finals. But ive totally removed dirty filters temporarily in the past till the new ones arrived because of low static pressure. Never had any problems like this.
    Southeastern Pa
    Quote Originally Posted by Onefast450r View Post
    Maybe I just don't do enough restaurant work, but I'm not sure what you mean by a "return fan." Do you by any chance mean makeup air unit?
    2 Tim 3:16-17
    Member, IAEI