Thread: Variable Speed Drive on Centrifugal Chiller

Hybrid View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Join Date
    Oct 2011
    Posts
    39
    Post Likes

    Variable Speed Drive on Centrifugal Chiller

    Is theer any risk of damage of the compressor, if VFD is installed for Trane Brand Centrifugal Chiller? The VFD's shall be install only to reduce inrush current. 650 Ton Centrifugal Chiller with 134A refrigerant and model is CVGF-0013.

  2. #2
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Trane sells VFDs with their chillers (at least in the U.S.) so they must believe it's O.K. York has been selling VFDs on centrifugal compressors for over 30 years. I believe the technology has been proven.

  3. #3
    Join Date
    Oct 2011
    Posts
    39
    Post Likes
    Thread Starter
    As I am suppling the VFD's and Chiller's are going to be supplied by another comapny, I was little bit confused, if there is any challenge to commission the VFD. I gues it should be like operating a fan motor through VFD, as our goal is to reduce the inrush current only.

  4. #4
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    184
    Post Likes
    You're going to feed an otherwise constant speed machine with a 3rd party VFD? Interesting. I wonder how the chiller's motor protection, etc. will react. Does Trane know about (and approve of) this installation?

    650 tons.... That's a pretty hefty VFD.

    Sent from my ADR6300 using Tapatalk 2

  5. #5
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by DDC_Dan View Post
    You're going to feed an otherwise constant speed machine with a 3rd party VFD? Interesting. I wonder how the chiller's motor protection, etc. will react. Does Trane know about (and approve of) this installation?

    650 tons.... That's a pretty hefty VFD.
    Putting third party VFDs on chillers is done frequently. Using it as a soft start only seems to be a waste of its potential, but there are many controls considerations that would have to be addressed to vary the speed while it's operating.

    I would guess the VFD will be around 500 HP. Not that large considering York offers an 1100 HP and ABB makes low voltage drives to 7500 HP.

  6. #6
    Join Date
    Feb 2013
    Location
    Phoenix, AZ
    Posts
    184
    Post Likes
    Quote Originally Posted by KnewYork View Post
    Putting third party VFDs on chillers is done frequently. Using it as a soft start only seems to be a waste of its potential, but there are many controls considerations that would have to be addressed to vary the speed while it's operating.

    I would guess the VFD will be around 500 HP. Not that large considering York offers an 1100 HP and ABB makes low voltage drives to 7500 HP.
    I guess I've lived a sheltered life, have never seen this done. Seems like a soft-starter would be more cost effective than a VFD.....

    One of my customers has a total of 6 York YK's, 900-ish tons each. Two were ordered as VSD, four were not. They are on an energy-saving kick, and plan to have the rest factory retrofitted to VSD's. They are also installing VFD's on everything in sight - CHW and CW pumps, Tower fans, just to experiment with various strategies.

  7. #7
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Why are you doing this? Are you in an area where starting the chiller with a traditional Wye-Delta or Solid State Starter would have an adverse effect on the power grid or other loads in the building? Using a VFD as a starter, i.e. ramping up to 60HZ and keeping it there is less efficient than just starting with a conventional electro-mechanical starter.

    I see no reason why it can't be done, but I am interested in knowing what you're trying to accomplish, because a VFD may not be the answer.
    Don't pick the fly crap out of the pepper.

  8. #8
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by Tech Rob
    Using a VFD as a starter, i.e. ramping up to 60HZ and keeping it there is less efficient than just starting with a conventional electro-mechanical starter.
    It is true that running a VFD at 60 Hz. consumes more than a conventional starter due to the losses in converting power from AC to DC and back to AC. I think if it were me, I'd fix the drive to run at 57-58 Hz. (IF I was going to employ the OP's strategy.)

    A VFD running at 55 Hz. is consuming 77% of the HP of the motor at 60 Hz. Even at 57 Hz. the HP is 85% of the rated HP. I would think there would be very few times that the chiller would be unable to make capacity when running at 57 Hz. What do you think? Would that work for this application?

  9. #9
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Quote Originally Posted by KnewYork View Post
    It is true that running a VFD at 60 Hz. consumes more than a conventional starter due to the losses in converting power from AC to DC and back to AC. I think if it were me, I'd fix the drive to run at 57-58 Hz. (IF I was going to employ the OP's strategy.)

    A VFD running at 55 Hz. is consuming 77% of the HP of the motor at 60 Hz. Even at 57 Hz. the HP is 85% of the rated HP. I would think there would be very few times that the chiller would be unable to make capacity when running at 57 Hz. What do you think? Would that work for this application?
    You make a great point. 57 Hz is 95% of the motor's rated speed. 90% of the savings that are to be had with a VFD are in the 50-60 Hz range. I think if the chiller ended up a little short on tonnage, it might be able to make up the difference by opening the vanes up a few degrees more or by running the condenser water a few degrees colder.
    Don't pick the fly crap out of the pepper.

  10. #10
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    I too am interested in knowing why you would do this for low inrush instead of a wye delta or soft starter.

  11. #11
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Quote Originally Posted by R123 View Post
    I too am interested in knowing why you would do this for low inrush instead of a wye delta or soft starter.
    There is terrific inrush with both of those starters when compared with a VSD. A VSD never pulls more than FLA, not true with wye-delta or solid state starter.

  12. #12
    Join Date
    May 2004
    Posts
    225
    Post Likes
    I could see a room for a big pissing match between manufacturer of unit ,drive ,installation contractor, and engineer if it's not selected properly Or fails to perform in anyway. All things being equal if you reduce the htz you may lose your lift, surges are tough on the bearings, stalls are tough on the whole machine!
    I know the guy who know's the "Chiller Whisperer"

  13. #13
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Quote Originally Posted by KnewYork View Post
    There is terrific inrush with both of those starters when compared with a VSD. A VSD never pulls more than FLA, not true with wye-delta or solid state starter.
    I know that. Like Tech Rob's asking, why is the inrush a problem? Is there issues with the electrical system not being able to handle the inrush? A VFD is a HUGE expense.

  14. #14
    Join Date
    Oct 2011
    Posts
    39
    Post Likes
    Thread Starter
    Electricity is the problem. There is huge power failure and needs to be depend on own generaation. If the VFD is not used, then the Generator sytem needs higher capacity.

  15. #15
    Join Date
    May 2004
    Posts
    225
    Post Likes
    As mentioned in previous posts, frequency drives are not new to chillers! When used properly they can do some amazing things I would just recommend that you consu lt with the manufacturer They may have accessory components that will lend it better for the application
    I know the guy who know's the "Chiller Whisperer"

  16. #16
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    I think one of the things that wasn't realized by the responders to this thread is that this chiller is not in the U.S. When Jubaer said the TRANE chiller had R134a in it I knew this chiller wasn't located in North America.

    The concerns about consulting the manufacturer are unfounded. Jubaer is just replacing one starter with another type. He clearly stated he wants to run at 60 Hz. So what difference does it make if he replaces a wye-delta starter with a VFD? Many VFDs have been put on chillers without checking with the manufacturer of the chiller. It's done all the time. If Jubaer wished to vary the frequency while running then he would have to have a way of controlling speed and vane opening.

    If the owner of the chiller isn't concerned about electrical costs past inrush then running at 60 Hz. Is fine. I think I would at least experiment with running at 55-57 Hz. as the upper limit. Money could be saved with little loss of capacity (if any).

  17. #17
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Quote Originally Posted by KnewYork View Post
    If the owner of the chiller isn't concerned about electrical costs past inrush then running at 60 Hz. Is fine. I think I would at least experiment with running at 55-57 Hz. as the upper limit. Money could be saved with little loss of capacity (if any).
    Agreed.
    Don't pick the fly crap out of the pepper.

  18. #18
    Join Date
    Oct 2011
    Posts
    39
    Post Likes
    Thread Starter
    Thanks KnewYork. My clients concern is just to reduce the inrush current. I am working with VFD's for FAN and PUMPS application long time but this is the first time with Chiller compressor. So just to check whether my step is ok or nor.

  19. #19
    Join Date
    May 2004
    Posts
    225
    Post Likes
    Why do some of us even bother? There's a reason why I only posted 100 times in 10 years!
    I know the guy who know's the "Chiller Whisperer"

  20. #20
    Join Date
    May 2004
    Posts
    225
    Post Likes
    I don't see where the OP clearly states it will be 60 hertz, Where is he located? What is the voltage and the cycles?
    I know the guy who know's the "Chiller Whisperer"

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •