    mini splits

    never really had to size a minisplit system. was wondering if it is the same as sizing a normal system or not anyone with any experiance doing this your help would be appreciated.

  2. #2
    Join Date
    Dec 2008
    Location
    Ontario Canada
    Posts
    543
    More or less its the same, due to capacity control, over sizing is not as big of a deal as with conventional splits.

    Air distribution is not quite as good, so multiple heads can be an effective fix for that

  3. #3
    Join Date
    May 2009
    Location
    In the Hudson Valley of New York
    Posts
    1,867
    I still size them to 100% heat gain and no more, I have had customers that wanted to go bigger, only to find the unit ran a couple degrees warmer then the setting to prevent it from shutting down and ending the dehumidifying process. The right size is always the size to install with any system. I like to sell absolute comfort, not peace of mind that it might not be big enough.

  4. #4
    Join Date
    Dec 2002
    Location
    Arizona
    Posts
    4,353
    Quote Originally Posted by Stevel6416 View Post
    never really had to size a minisplit system. was wondering if it is the same as sizing a normal system or not anyone with any experiance doing this your help would be appreciated.
    Keep in mind there is no duct loss.
    Make your expertise uniquely valuable.

    Make your influence uniquely far-reaching.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event