    hobert diswasher

    M#Lx1h PROBLEM IS NOT HOT ENOUGH WHEN IT IS RENSE CYCLE .
    AFTER DELIMED.
    WASH CYCLE IS 164 DEGREE(do not rem. to make the 0) and the tool and p2 display and rinse about 120 degree.
    How can I reset the sign and what is the problem
    Thankyou!

  2. #2
    Join Date
    Jan 2007
    Posts
    166
    Asked the hobert tech.He told me is the rinse probe.But I replaced the wash probe ,there are three probes I do replaced the wrong one.The one rince probe is at the back of diswasher.
    And have been delimed 3x.Now I delime it over night, see how it work?

  3. #3
    Join Date
    Jan 2007
    Posts
    166
    Hobart still the sam preblen,190 but sensor display 50 degree under

  4. #4
    Join Date
    Jan 2007
    Posts
    166
    Replaced the senser at the back.BINGO