    Quote Originally Posted by jmac00 View Post
    it's quite possible that the building inspector doesn't have a clue about the NEC

    But no one has complained yet,
    That is certainly a possibility, since many inspectors use the IRC (International Residential Code) which sources some, but not all of the NEC residential rules.

    It is VERY possible that he is completely unaware of much of the NEC.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  2. #15
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    23,915
    Post Likes
    Just an FYI: if the controls section of a condenser faces the building, the distance from the building must be 3' 6" according to NEC 110.26 A, with condition 2 in play.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  3. #16
    Join Date
    Oct 2014
    Location
    Central Kentucky
    Posts
    27
    Post Likes
    The meter is property of the utility company, it is not utilization equipment which is covered by the NEC. Our local power company hands you a sheet when you pick up the meter base with some basic requirements like center line of the meter (not the base) is no less than 4' or more than 6' above finished grade level. They also send a rep out to approve the meter location before you set it. They mostly want to make sure it has easy and safe access for their meter readers. They don't want them to have to walk across sidewalks that might be iced over, be responsible for opening and closing gates, or battling overgrown landscaping, etc. Obviously meter location can have a substantial cost impact on the job. If you have to extend the service entrance any more than putting a conduit nipple out of the meter base through the exterior wall to the service panel, you have to install an outdoor weatherproof service disconnect which in addition to being expensive its ugly too. Our power company has been very good to work with in my experiences.

  4. #17
    Join Date
    Jan 2010
    Posts
    10,296
    Post Likes
    Quote Originally Posted by bourbon View Post
    If you have to extend the service entrance any more than putting a conduit nipple out of the meter base through the exterior wall to the service panel, you have to install an outdoor weatherproof service disconnect which in addition to being expensive its ugly too.
    I had a conversation with an electrician a while back about this. I asked him why, on his new service install, there was not a main breaker at the indoor panel. Instead it was on the outside of the house. He told me the code dictated if the indoor panel was not within x amount of the point of entrance it had to be outside. Why is this ?

  5. #18
    Join Date
    Aug 2014
    Location
    DC suburbs
    Posts
    310
    Post Likes
    Quote Originally Posted by VTP99 View Post
    I had a conversation with an electrician a while back about this. I asked him why, on his new service install, there was not a main breaker at the indoor panel. Instead it was on the outside of the house. He told me the code dictated if the indoor panel was not within x amount of the point of entrance it had to be outside. Why is this ?
    The cable to the service panel is unfused except for the high voltage fuse at the transformer which is often grossly over sized to prevent nuisance trips. They want to limit how much of this unfused cable is inside of a structure. Unless it feeds directly into the rear of the interior panel there will always be some so it's kind of a compromise, making it as safe as reasonably possible.