    Trouble shooting a customers 19XRV. Prestart failure on High line voltage. Panel shows 200-1000v jumps around. Incoming is rock steady at 480v.
    Trouble shot panel with power off, now alarms with reverse phase?
    Power and phasing is normal, anyone seen this? I'm guessing the ISM board. But that is a $2100 guess, Any help is appreciated
    Greg
    East of big city prices.
    Me thinks you need to remove your pricing per the rules.
    Nov 2012
    Minnesota
    I don't see how to edit? Oops.
    Greenville SC
    Most likely the ISM
    Nov 2010
    Im sure you already fixed this but i have replaced 2 isms for the same reason in the past 5 years on the same 19xrv. Just thought id post for others
    May 2012
    California
    Most likley ISM
    Southern NJ
    You could even have something as simple as a loose connection on the communication wiring connecting all the control boards, or corrosion on a pin connecting a sensor to a board. In my experience I have noticed Carrier chillers to be very prone to nuisance faults that do not actually exist. I would check every connection on every board before replacing components. I wish you luck.