    Confused 30XA Air cooled Carrier Chiller Economizer leaks

    I have a 30 Xa air cooled carrier chiller, the economizer has had leaks occur on the exit to the compressor around the stainless steel stub. The copper pipe work has also cracked around the pressure relief valve.

    It has been replaced and 5 months later the economizer has another leak on the new economizer in the same spot. The compressor has been monitored at different hz to check for unwanted vibration.

    Has anyone had the same issue or can shed any light on the above problem?

    TD

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    How about some pictures and maybe a better model and serial number? How old is this chiller?

  3. #3
    Join Date
    Oct 2011
    Location
    South Georgia
    Posts
    141
    Post Likes
    Is there a muffler installed in the economizer line piping between the BPHC and the compressor?

  4. #4
    Join Date
    Apr 2007
    Location
    uk
    Posts
    326
    Post Likes
    I have seen a couple of leaks around the pressure relief valve at the econimizer usually due to an inadequate silver soldered joint.

  5. #5
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by Gibbo View Post
    I have seen a couple of leaks around the pressure relief valve at the econimizer usually due to an inadequate silver soldered joint.
    You talking about the thermal relief Gibbo?

  6. #6
    Join Date
    Jun 2007
    Location
    NY
    Posts
    48
    Post Likes
    We have 2 under contract. I haven't seen any leaks at that spot specifically, but the 2 that I have are leaky disasters. O-ring failures, suction service valve failures, micro-channel condenser coil cracks. Good full-maintenance contract. LOL.

  7. #7
    Join Date
    Nov 2012
    Posts
    9
    Post Likes
    Thread Starter
    Yes the condenser coils are a common failure, once they have been replaced with the new coils they seem to have no issues....fingers crossed.

  8. #8
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    welding is correct that you used to weld the economizer.

    when soldering the economizer withhold the relief valve?

  9. #9
    Join Date
    Nov 2012
    Posts
    9
    Post Likes
    Thread Starter
    Hi servicetrane,

    The relief valve was removed when welding the new econimizer into place. The initial leak was around the relief valve base. This was repaired and then a leak appeared around the stainless steel stub on the heat exchange approx 1 month later.

    The heat exchange was replaced with a new one, then 5 months later a leak has appeared in the same spot on the new heat exchange? I have come accross the condenser coils leaking but not the heat exchange.

  10. #10
    Join Date
    Nov 2012
    Posts
    9
    Post Likes
    Thread Starter
    Hi Guys, attached are a couple of photos and the full model number.

    Model number - 30XA0902-0158-PEE
    2008 year of Manufacture.


    One photo will show the whole econimizer sub assembly, the other will show the leak on the stainless steel stub.Click image for larger version. 

Name:	30XA - Carrier.jpeg 
Views:	69 
Size:	114.7 KB 
ID:	381241Click image for larger version. 

Name:	30XA.jpeg 
Views:	68 
Size:	114.7 KB 
ID:	381251

  11. #11
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    That appears to be European machine to me is the cooler DX?
    What part of the globe are you in?

    I have never seen that kind of leak leak on a BPHE. There should be a muffler and pipe clamps on that line

    Seems like a very odd occurrence to me.

    Quote Originally Posted by Kinky copper View Post
    Hi Guys, attached are a couple of photos and the full model number.

    Model number - 30XA0902-0158-PEE
    2008 year of Manufacture.


    One photo will show the whole econimizer sub assembly, the other will show the leak on the stainless steel stub.Click image for larger version. 

Name:	30XA - Carrier.jpeg 
Views:	69 
Size:	114.7 KB 
ID:	381241Click image for larger version. 

Name:	30XA.jpeg 
Views:	68 
Size:	114.7 KB 
ID:	381251

  12. #12
    Join Date
    Nov 2012
    Posts
    9
    Post Likes
    Thread Starter
    Yes cooler is DX.

    Australia - Queensland

  13. #13
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    you may need the pipe vibration that damages economizer and economizer.

    you changed the muffler the economizer line to the compressor?

  14. #14
    Join Date
    Apr 2007
    Location
    uk
    Posts
    326
    Post Likes
    Yes it looks like a French made chiller due to the model number, also looks like piping has been changed too the PRV leaks are usually on the stub brazed onto the pipe not the PRV itself. Never seen or heard of the econimizer stub leaking before will check it out.

  15. #15
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes

  16. Likes toptech liked this post.
  17. #16
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    wierd, i just had a cust call and tell me that he has a leak in the stub of the econ, I told him that I've never seen that and then this. whats the odds.

  18. #17
    Join Date
    Nov 2012
    Posts
    9
    Post Likes
    Thread Starter
    Hi Nique,

    from my attached photos is the leak on the same line?

  19. #18
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    not sure, I was on the phone as I was reading this. I will be heading up in the next few days to check it out.

  20. #19
    Join Date
    Nov 2012
    Posts
    9
    Post Likes
    Thread Starter
    ok, it would be interesting to see if it is in the same location.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •