  1. #1
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    346
    Post Likes

    Hmm cvhe250, 1989 vintage model

    what would cause the compressor discharge temperature to run hot around 160 degrees at 45 % load. there is no issue with condenser or evaporator water flow,no non condensibles, charged was weighed in with a micron test of 500 microns. chiller makes capacity just notice the discharge runs hot and the economizer pipe nearest to the discharge is also very warm. any ideas???

  2. #2
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    aproach which is the condenser?

  3. #3
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    346
    Post Likes
    Thread Starter
    1-2 degrees

  4. #4
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    readings of the machine will have in operation?

  5. #5
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    Post a complete log.

  6. #6
    Join Date
    Aug 2000
    Location
    Under my tree
    Posts
    5,133
    Post Likes
    Its running unloaded, not a large enough volume of gas to cool the discharge down. Once it loads up the discharge temp will drop.
    To much work with too little time!!!!

  7. #7
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    In my experience R-11 machines, and particularly small R-11 CVHEs run high discharge temps to begin with. When you say 45% loaded, are you talking about %RLA or is 45% an approximation of the vane position? If it's 45% RLA, the chiller's unloaded and that's why your discharge temp is high.
    Don't pick the fly crap out of the pepper.

  8. #8
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    346
    Post Likes
    Thread Starter
    I figured unloaded was the issue, it is a r11 machine, when i ruled out the noncondensibles it made sense, however ive seen other machine similar run between100 to 125 degrees. I know the carrier 19dk are famous for getting hot when they have noncondensibles. Ill load it up and test it once again. The building added rtus for some areas which took load off the chiller.....ill follow up
    By the way all the approaches ard right on the money.

  9. #9
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    346
    Post Likes
    Thread Starter
    Thanks guys

  10. #10
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    You're welcome.
    Don't pick the fly crap out of the pepper.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •