    Confused 30XA Air cooled Carrier Chiller Economizer leaks
    I have a 30 Xa air cooled carrier chiller, the economizer has had leaks occur on the exit to the compressor around the stainless steel stub. The copper pipe work has also cracked around the pressure relief valve.
    It has been replaced and 5 months later the economizer has another leak on the new economizer in the same spot. The compressor has been monitored at different hz to check for unwanted vibration.
    Has anyone had the same issue or can shed any light on the above problem?
    TD
    East of big city prices.
    How about some pictures and maybe a better model and serial number? How old is this chiller?
    Oct 2011
    South Georgia
    Is there a muffler installed in the economizer line piping between the BPHC and the compressor?
    uk
    I have seen a couple of leaks around the pressure relief valve at the econimizer usually due to an inadequate silver soldered joint.
    Quote Originally Posted by Gibbo View Post
    You talking about the thermal relief Gibbo?
    Jun 2007
    NY
    We have 2 under contract. I haven't seen any leaks at that spot specifically, but the 2 that I have are leaky disasters. O-ring failures, suction service valve failures, micro-channel condenser coil cracks. Good full-maintenance contract. LOL.
    MEXICO
    welding is correct that you used to weld the economizer.
    when soldering the economizer withhold the relief valve?
    Nov 2012
    Hi Guys, attached are a couple of photos and the full model number.
    Model number - 30XA0902-0158-PEE
    2008 year of Manufacture.
    One photo will show the whole econimizer sub assembly, the other will show the leak on the stainless steel stub.30XA - Carrier.jpeg30XA.jpeg
    Nov 2012
    Hi servicetrane,
    The relief valve was removed when welding the new econimizer into place. The initial leak was around the relief valve base. This was repaired and then a leak appeared around the stainless steel stub on the heat exchange approx 1 month later.
    The heat exchange was replaced with a new one, then 5 months later a leak has appeared in the same spot on the new heat exchange? I have come accross the condenser coils leaking but not the heat exchange.
    Nov 2012
    Yes the condenser coils are a common failure, once they have been replaced with the new coils they seem to have no issues....fingers crossed.
    That appears to be European machine to me is the cooler DX?
    What part of the globe are you in?
    I have never seen that kind of leak leak on a BPHE. There should be a muffler and pipe clamps on that line
    Seems like a very odd occurrence to me.
    Quote Originally Posted by Kinky copper View Post
    MEXICO
    you may need the pipe vibration that damages economizer and economizer.
    you changed the muffler the economizer line to the compressor?
    uk
    Yes it looks like a French made chiller due to the model number, also looks like piping has been changed too the PRV leaks are usually on the stub brazed onto the pipe not the PRV itself. Never seen or heard of the econimizer stub leaking before will check it out.