Results 1 to 9 of 9
  1. #1
    Join Date
    Jun 2006
    Posts
    278

    Delta to Jace integration

    Hi all
    I have a site that has a Orcaview work station connected to a Delta DSC1616 thru ethernet connection then a bus going out to 8 controllers on ahi's and roof tops and 2 vav controllers. The customer wants a jace like their other buildings and I am looking for the best way to integrate.
    They would like to keep as much of the existing system to start then we can go to something open over time.
    Thanks
    in advance
    Kevin

  2. #2
    Join Date
    Oct 2009
    Posts
    572
    Im not familiar with the Delta stuff but I tried to integrate to it with a jace also. The site ended up being Deltas own proprietary protocol called V2, there isn't a driver that im aware of for AX. If its bacnet it should work though.

  3. #3
    Join Date
    Sep 2009
    Location
    Michigan
    Posts
    21
    You Will be able to tie this into a Jace, all you need is the Bacnet license.

  4. #4
    Join Date
    Jun 2006
    Posts
    278
    Quote Originally Posted by Lapham636 View Post
    You Will be able to tie this into a Jace, all you need is the Bacnet license.
    I tried on the ethernet side and I had no luck. Were you saying I should be on the mstp side?

    Sent from my SPH-L710 using Tapatalk 2

  5. #5
    Join Date
    Feb 2007
    Location
    Helena, Montana
    Posts
    1,967
    No you should be able to find them on the ethernet side. What Lapham is saying is that your JACE has to be licensed and configured for BACnet. Is this Ax or R2?
    Don't worry zombies are looking for brains, you're safe...

  6. #6
    Join Date
    Jun 2006
    Posts
    278
    Ax and I am using workbench so there are no licensing issues.
    I couldn't get the dsc to show up, but I dont know the network number. Could I see everything from the mstp side? Is there a tech doc for the Delta ingratiation?

  7. #7
    Join Date
    Feb 2007
    Location
    Helena, Montana
    Posts
    1,967
    I believe you need to know the network number. If you go into BACnet device manager and do a discover, nothing shows up? I'm not sure that just because it is AX, that BACnet is automatically licensed. I have several that are only LON and they do not have the BACnet "feature" called out in the license file.
    Don't worry zombies are looking for brains, you're safe...

  8. #8
    Join Date
    Jun 2006
    Posts
    278
    in the Orcaview settings the network number is set to 0 and the jace cant take a network number of 0. the license file is fine

  9. #9
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,324
    So bacnet shows up in your license file???????
    UA Local 141