Results 1 to 13 of 17
    Trane RTU advice
    Mod YCD108BH0EA
    #m4010265 from 1997
    Unit has a progammable t-stat/zone sensor, tenant in the store wants reg old thermostat so it's easier to operate.
    I am somewhat familiar with the newer Trane reliatel but this unit appears to have 24 volts at the stat?
    I called Trane and got the impression the counter guy wasn't sure which stat would replace that one.
    He quoted me on a FEN004120 single point stat.
    But like I said, I got the impressioin he wasn't real sure.
    So does that system operate on 24 volts and any idea what reg zone sensor will work with it?
    Hey cockroach, don't bug me! ©
    Sep 2006
    Winter Springs, Fl
    dice: what is the unit/ tstat pinout? what colors go where? are the wires landed on a circuit card similar to a reliatel card or is it some kinda funky thing in there. do you have the existing tstat mod# available?
    If you can't learn to do something well, learn to enjoy doing it poorly.
    VETO PRO PAC - The Official Tool Bag of HVAC-Talk.com
    Philly
    Courtesy of another member
    http://www.hvac.amickracing.com/RTU%...r%20Micro1.pdf
    Hope I'm not out of line.
    Rapid City, SD
    It's been to long since I've worked on a RTU...
    But I'm pretty sure some of the Trane RTU's can use both 24v and the other less complicated system.
    Most likely you can just get a regular stat and mount it up.
    Course... I'm rambling, and it wouldn't hurt to research or wait for someone to verify this before you try said advice.
    S.E. North Carolina Coast
    Dice,
    I believe the older Tranes' require a thermostat interface board ( $ 150.00 )
    in order to hook up a standard thermostat ( $ 40.00 ).
    That OEM programable zone sensor (T-stat) is $$$ . Maybe with your good looks and charm you can explain to your customer that replacing that zone sensor isn't such a good idea from a cost standpoint, but if they're willing to spend $ 600.00 you will be more than happy to help them.
    Your Trane counter dude should be able to make you a free copy of the programable zone sensor instruction manual to help you reprogram your customers current T-stat.
    It's funny how many of my customers have these programable zone sensors and are intimidated by the up and down arrow buttons... Then again whoever designed these for Trane needs to be slapped above the shoulders profusely
    Wisconsin
    You need a conventional thermostat interface board. It comes with a cable that you plug into the main board and a print that shows the terminal strip designations.
    No books with the unit and the wiring diagram is faded......of course.
    It's 10 years old and I'm sure you can't hook up a reg stat like the newer units.
    I believe the guys are on target about the interface board but what about keeping the exisiting set up and just installing a non-programmable zone sensor?
    Thanks a lot.
    Spoke to Trane service rep today.
    Says to use a BAYSENS008B stat.
    Use 5 wires, 1-2-3-4-5.
    Found out the 24 volts at the stat is to power the existing thermostat and those wires can be eliminated.
    hmmmmmmmmm
    After all that............
    They said to program the stat for em and see what goes.
    OK all done, works good, showed them how to over ride but told them not to touch it otherwise.
    Thanks for the help, I learned something and got to charge for it too.
    OJT, if you are doing it for free, you need a new career.
    Jun 2006
    Get a Trane TCI board and a conventional stat. Dick and Jane. Ken
    Wisconsin
    Quote Originally Posted by joken View Post
    TCI is a communication board
    Their corporate doesn't want to spring for a new set up.
    I took my time and set up the stat, which is pretty nice by the way.
    And showed the manger how to use it, and told eveyone else not to touch it.