    Something's missing

    Name:  ImageUploadedByTapatalk1367621130.131160.jpg
Views: 1426
Size:  90.0 KB

    Got called out to look at a walk in at a gas station and found this gem. We got outbid on the condenser install and this is what they got. See anything missing?

    Evap coil was not changed, and old unit had burnt up compressor.

  2. #2
    Join Date
    Jan 2013
    Location
    New Jersey
    Posts
    33
    Liquid and suction drier?

  3. #3
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    2,020
    Im guessing a disconnect?

  4. #4
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    106
    Yup, filter driers. They installed the new condenser and put no filters on at all.

  5. #5
    Join Date
    Aug 2012
    Posts
    2,576
    Filter could be out of sight. defiantly should have a suction line FD. Disconnect could be within eyeshot.
    My name is TooCoolforschool and I am a chronic over charger.

  6. #6
    Join Date
    Jan 2013
    Location
    New Jersey
    Posts
    33
    Well they'll be replacing it soon again anyway. Maybe you get the bid next time. Or with any luck a compressor change.

  7. #7
    Join Date
    Jan 2004
    Location
    Here and there
    Posts
    4,802
    I always like the liquid drier inside by the evap.
    i belong to peta ... people eating tasty animals. all my opinions are just mine.

  8. #8
    Join Date
    Dec 2011
    Location
    Grass Lake, MI
    Posts
    251
    Quote Originally Posted by jpb2 View Post
    I always like the liquid drier inside by the evap.
    I'm with jpb2. Most manufactures require LLD installation as close to the metering devise as possible. I should not expect to see the LLD in the pic nor should I expect to see a SLD because they came and removed it like they should!

  9. #9
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    106
    Checked inside at the Evap. Wasn't touched. They left the old lines to the inside and just brazed new ends at the compressor

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,259
    If that's for a walk-in box, there's a lot more missing than just a filter-drier.

  11. #11
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    106
    No that's ac for the store. We were just there to look at the walk in. I worded that wrong.

    Probably should have had a cycle switch or some type of pressure control since it was 40 degrees today and running I would guess though.

  12. #12
    Join Date
    Oct 2012
    Location
    Smallville
    Posts
    106
    And yea it had a disconnect.

  13. #13
    Join Date
    Apr 2013
    Location
    Knoxville TN
    Posts
    53
    Some of those condenser have FD inside the cond.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event