Something's missing

Got called out to look at a walk in at a gas station and found this gem. We got outbid on the condenser install and this is what they got. See anything missing?
Evap coil was not changed, and old unit had burnt up compressor.
-
Liquid and suction drier?
-
Im guessing a disconnect?
-
Yup, filter driers. They installed the new condenser and put no filters on at all.
-
Filter could be out of sight. defiantly should have a suction line FD. Disconnect could be within eyeshot.
It's not if your doing it right it's whether your doing the right thing that is important.
-
Well they'll be replacing it soon again anyway. Maybe you get the bid next time. Or with any luck a compressor change.
-
I always like the liquid drier inside by the evap.
-
 Originally Posted by jpb2
I always like the liquid drier inside by the evap.
I'm with jpb2. Most manufactures require LLD installation as close to the metering devise as possible. I should not expect to see the LLD in the pic nor should I expect to see a SLD because they came and removed it like they should!
-
Checked inside at the Evap. Wasn't touched. They left the old lines to the inside and just brazed new ends at the compressor
-
If that's for a walk-in box, there's a lot more missing than just a filter-drier.
-
No that's ac for the store. We were just there to look at the walk in. I worded that wrong.
Probably should have had a cycle switch or some type of pressure control since it was 40 degrees today and running I would guess though.
-
And yea it had a disconnect.
-
Some of those condenser have FD inside the cond.