Results 1 to 13 of 30
    Oct 2012
    Smallville
    Something's missing
    Got called out to look at a walk in at a gas station and found this gem. We got outbid on the condenser install and this is what they got. See anything missing?
    Evap coil was not changed, and old unit had burnt up compressor.
    Jan 2013
    New Jersey
    Liquid and suction drier?
    Dec 2012
    columbus, OH
    Im guessing a disconnect?
    Oct 2012
    Smallville
    Yup, filter driers. They installed the new condenser and put no filters on at all.
    Aug 2012
    Filter could be out of sight. defiantly should have a suction line FD. Disconnect could be within eyeshot.
    It's not if your doing it right it's whether your doing the right thing that is important.
    Jan 2013
    New Jersey
    Well they'll be replacing it soon again anyway. Maybe you get the bid next time. Or with any luck a compressor change.
    Here and there
    I always like the liquid drier inside by the evap.
    Oct 2012
    Smallville
    Checked inside at the Evap. Wasn't touched. They left the old lines to the inside and just brazed new ends at the compressor
    Jul 2000
    Guayaquil, EC
    If that's for a walk-in box, there's a lot more missing than just a filter-drier.
    Oct 2012
    Smallville
    No that's ac for the store. We were just there to look at the walk in. I worded that wrong.
    Probably should have had a cycle switch or some type of pressure control since it was 40 degrees today and running I would guess though.
    Oct 2012
    Smallville
    And yea it had a disconnect.
    Apr 2013
    Knoxville TN
    Some of those condenser have FD inside the cond.
    Atlanta GA area
    I do not see any low voltage wiring... Is it inside the conduit with the high voltage wiring (not legal in my state unless the wire is insulated for high voltage).
    GA-HVAC-Tech