Results 1 to 9 of 9

Hybrid View

  1. #1
    Join Date
    May 2013
    Location
    N.W. Wisconsin
    Posts
    3
    Post Likes

    Return Air through the back of the Furnace

    I'm going to install a furnace at my cabin (about 700 sq. ft.). One great room, two bed rooms, a full bathroom and a small utility closet. The ceilings are eight feet high, the windows are Anderson low-e glass double pane, and the insulation is up to code as well.

    The current furnace is is installed in tight quarters in the utility closet, the return air is currently in the back of the furnace and then goes into the great room only.

    The old furnace is adequate and works fine, but it is over 30 years old and is time to replace, along with adding a/c.

    I'm going to replace it with a 80% Goodman GMH80603AN and a CAPF1824A6DB case coil and a GSX130241 condensor. The manual says not to have the return air off of the back of the furnace. It can go off of the sides or come in from the bottom. I guess I don't understand why this can't be taken off of the back? This would make an easy installation for me if that could be done.

    My only option is to make an enclosed furnace stand (like an air handler stand) elevate the furnace on top of the stand and connect it to my current return air in the back of the closet correct?

    Thanks for your help,
    Nate

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,095
    Post Likes
    Quote Originally Posted by nhmort View Post
    I'm going to install a furnace at my cabin (about 700 sq. ft.). One great room, two bed rooms, a full bathroom and a small utility closet. The ceilings are eight feet high, the windows are Anderson low-e glass double pane, and the insulation is up to code as well.

    The current furnace is is installed in tight quarters in the utility closet, the return air is currently in the back of the furnace and then goes into the great room only.

    The old furnace is adequate and works fine, but it is over 30 years old and is time to replace, along with adding a/c.

    I'm going to replace it with a 80% Goodman GMH80603AN and a CAPF1824A6DB case coil and a GSX130241 condensor. The manual says not to have the return air off of the back of the furnace. It can go off of the sides or come in from the bottom. I guess I don't understand why this can't be taken off of the back? This would make an easy installation for me if that could be done.

    My only option is to make an enclosed furnace stand (like an air handler stand) elevate the furnace on top of the stand and connect it to my current return air in the back of the closet correct?

    Thanks for your help,
    Nate
    The fan housing will block the majority of the opening

  3. #3
    Join Date
    Dec 2010
    Location
    The Quad-Cities area (midwest).
    Posts
    2,744
    Post Likes
    To elevate the new furnace will not only be the correct way to do it, but it'll also make for a more quiet installation. The new furnace will move much more air, thus it'll be really noisy. If you have the height, put a filter rack underneath the furnace. The shallow ones a good for 1" or 2" filters.

  4. #4
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    310
    Post Likes
    Build an insulated, elevated stand it will work better and it will be quieter.

  5. #5
    Join Date
    May 2012
    Location
    San Diego, CA
    Posts
    352
    Post Likes
    Ditto, always listen to the manufacturer and don't do anything that can void the warranty like creating an opening in the back.
    You can call me Sam

    It should be a crime to be a mechanical engineer in San Diego
    Summer Design Temperature: 83 F Dry Bulb ~ 69 F Wet Bulb (California Climate Zone 7)

  6. #6
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    7,533
    Post Likes
    why such a big furnace for 700 sq ft a 45000 btu furnace should be plenty .also the new furnace should be much shorter .need to figure a way to redo the return .
    Go Trump

  7. #7
    Join Date
    May 2013
    Location
    N.W. Wisconsin
    Posts
    3
    Post Likes
    Thread Starter
    Thanks for all of your help.

    I will build an elevated stand that's insulated.

    We have a 3 season porch that's 220 sq. ft. It's insulated but has screens. I'm going to put in windows to make it a 4 season porch. Thus the higher BTU furnace.


    Thanks for the information

  8. #8
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,244
    Post Likes
    Still beg to question y so biggg?

  9. #9
    Join Date
    May 2013
    Location
    N.W. Wisconsin
    Posts
    3
    Post Likes
    Thread Starter
    So the real question without using manual J or D calculations, I looked online and asked other people for correct sizing of my system.

    I figured that 60,000BTU at 80% efficiency net output is 48,000BTU. Plus, its a 2 stage so it will usually run on the 1st stage most of the time. I usually don't heat the cabin in the winter, so if I do decide to heat it when I'm there, I figure that it will heat the place faster. My current unit is 50,000BTU and is over 30 years old, so I assume the efficiency is less that 80% and that's not doing a great job on initial heating. I took five hours to heat it from 20 degrees to 70 degrees last winter.

    I realize its a little large, but I got one heck of a deal for this system, I couldn't pass it up. It was $ shipped to my house.

    Thanks, Nate
    Last edited by jpsmith1cm; 05-09-2013 at 09:49 PM. Reason: removed pricing

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.