    My home is about 3,100 sq ft on two floors with a single open staircase at the front of the house. I done a Manual J using HVAC-Calc inputting my current configuration and then re-running it after making changes to the home like more insulation and reducing infiltration. Therefore, I have an as is and an as will be analysis.
    The current as-is results show that the home has heat loss/gain as follows:
    Heat loss: 49,877 First floor
    41,967 Second floor
    91,920 Total Heat Loss
    Heat Gain: 26,565 (20,506 Sen) First floor
    21,099 (18,310 Sen) Second floor
    47,965 (38,830 Sen) Total Heat Gain
    The as will be results are:
    Heat loss: 43,680 First floor
    33,586 Second floor
    77,324 Total Heat Loss
    Heat Gain: 24,217 (18,440 Sen) First floor
    17,568 (15,475 Sen) Second floor
    41,801 (34,923 Sen) Total Heat Gain
    My current equipment is as follows
    First Floor:
    Oil fired hot air furnace rated output 86,000 BTU
    Cooling with 2.5T York A/C (single stage)
    Second Floor:
    York 3T heat pump (single stage) strips used only for defrost
    Here is what I am trying to figure out from the Man J calculation.
    My current as is configuration calls for nearly equal heat loss for both the first and second floors at the design temp of 0*. But, the real world configuration shows that the first floor oil furnace is providing the majority of both the first and second floor requirements. In making this statement I am assuming that the heat pump has output of around 10K BTU when the outside temp is around 5*, the low that we have had this winter. I should note that the house has even temps from room to room and maintains the set point when the OD temp is 5*.
    Similarly, while the Man J calls for more cooling on the first floor than the second, the reality is the second floor heat pump is larger than the first floor A/C and, in fact, provides the majority of the cooling for the entire house. When at or near the summer design temp of 96* the heat pump is running continuously but the first floor A/C is cycling albeit not a lot. As during the winter months the home is generally comfortable during the summer with consistant room temps and the set point being maintained.
    I understand the physics of heat rising in the winter and cool air falling during the summer, but when it comes time to replace equipment how should it be sized? If the equipment were sized for cooling based on the Man J, it appears as though from real world experince the second floor is going to be warm while the first floor unit will constantly short cycle. Also, it looks like the heat requirements would not be met if the Man J is followed as the heat second floor unit would short cycle while the first floor unit could never meet demand.
    It seems like when there are upper and lower zones, each with separate equipment and controls, then the burden of the heating and cooling must shift accordingly. Im interested in real world experience and comments.
    Huntsville,AL
    go with the facts -- from the real world, your existing systems --
    SW FL
    Thumbs up
    Quote Originally Posted by mchild View Post
    My home is about 3,100 sq ft on two floors with a single open staircase at the front of the house. I have performed a Manual J using HVAC-Calc
    41,967 Second floor
    ... the first floor oil furnace is providing the majority of both the first and second floor requirements.
    Similarly, while the Man J calls for more cooling on the first floor than the second, the reality is ...
    ... consistent room temps and the set point being maintained.
    It looks quite obvious that the loads on the 1st and 2nd floors
    are identical for Practical purposes.
    Manual J is a nice guideline
    Designer Dan
    Sep 2006
    So I should expect for any heating equipment that is located on the first floor to continue to provide the majority of the heat requirement and similarily the cooling requirement will be primarily carried by the second floor unit.
    Therefore, the reports are more helpful in the total heat gain/loss and equipment sizing should be weighted to the where it is located.
    Feb 2007
    Did you use the free download? I'm not real sure, but I don't think you can change your climate variables w/ that version.
    Sep 2006
    No I used the HO version. Set the summer temp at 96 winter at 0 and grains 107.