Results 1 to 13 of 17
    Jun 2008
    NC
    Using resistor to convert to 4-20ma to 1-5v
    When placing a resistor in the 4-20ma to convert it to voltage is it placed in series or parallel?
    When placing it in parallel i get no voltage at the inputs. I run the 4-20ma signal into the analog input, with the common of the 24vdc to the common of the controller, then place the resistor between the common and analog input of the controller. This results in nothing
    When placing the 4-20ma signal into one end of the resistor and out the other end i got 7 volts which makes no sense since its a 250ohm resistor. I should be reading around 1.5-2vlts (ma output is 6.21) Either the resistor is bad or ??
    Also, how do you figure out the wattage of the resistor to use??
    Also had to just flip dipswitches to convert prior to this
    thanks!
    New England
    Ive never used a resistor for a AI usually only on AO. It seems like you had it installed correctly.
    "The bitterness of poor quality remains long after the sweetness of low price is forgotten". --Benjamin Franklin
    Georgia
    Quote Originally Posted by Shockwave View Post
    thanks!
    Is this 4-20 with a two wire connection?
    Jun 2008
    NC
    Quote Originally Posted by chadtech View Post
    Yes a two wire
    wattage i figured out, max volts squared divided by resistor value = watts
    Jul 2009
    Kansas
    Feb 2013
    Phoenix, AZ
    Here is the normal hookup for a 2-wire 4-20ma instrument converted to 1-5V at the controller (resistor is 250 ohm):
    Mar 2012
    WV
    I use a 500ohm and just go across the two wires at the device that is controlling the device.One side on positive one side on negative. If that makes sense. Works everytime. Also this will not work the other way around
    Mar 2012
    WV
    Oh sorry buddy.. that for 4-20 to 0-10VDC I read your post wrong
    Dec 2008
    Ontario Canada
    500 ohm resistor will work, however most manufactures I believe use 570. This will give 2-10VDC not 0-10. Wattage shouldn't matter, as amp draw is almost nonexistent. It's a resistive circuit, so ohms law applies.
    Feb 2013
    Phoenix, AZ
    Quote Originally Posted by LKJoel View Post
    If Ohm's law applies, (and it does), then 570 ohms will not give the expected results:
    At 4ma:
    E = I R
    E = 0.004 X 570
    E = 2.28V
    At 20ma:
    E = 0.02 X 570
    E = 11.4V
    The load resistance needs to be 500 ohms for 2-10V and 250 ohms for 1-5V.
    wattage is:
    P = I^2 X R
    P = 0.02^2 X 250
    P = 0.1 W
    P = 0.02^2 X 500
    P = 0.2 W
    In both cases wattage is less than 1/4W, but the 500 ohm resistor is close, and will get warm (at 20ma).
    Amarillo by mornin'
    "It's not that I'm smart, it's that I stay with the problem longer”
    Albert Einstein
    Dec 2008
    Ontario Canada
    Quote Originally Posted by DDC_Dan View Post
    At 4ma:
    E = I R
    E = 0.004 X 570
    E = 2.28V
    At 20ma:
    E = 0.02 X 570
    E = 11.4V
    (at 20ma).
    I am we'll aware of how ohms law works. And of course the "correct" answer is 500 ohms. I do however know that I have seen in several applications where manufacturers have used a 570 ohm resistor to preform the same function. Don't know why, if anybody does know I would appreciate an answer
    Feb 2013
    Phoenix, AZ
    Could you give an example of one? I have not run across this, would be interesting to examine.
Comfortech Show Promo Image
Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event