    Feb 2007
    Question trying to understand airflow of existing system
    I am trying to learn enough about HVAC design principles to understand the state of my HVAC.
    Today, I am focusing on airflow on the second floor of a 2-story traditional colonial house over an unconditioned basement.
    I am about to install a foot of blown-in insulation in the attic which will make future access to ductwork difficult. While surverying the attic for the insulation install, I have finally also looked at what I suspect is an unbalanced duct design.
    The east-most room is over a garage and is 5-degrees colder in the heating season and about 5 degrees warmer in the cooling season. On the other extreme is a bathroom consisting of two small rooms, each one blasted by a short duct run from the nearby supply plenum.
    Here is what is in the attic:
    Air Handler: Trane XV80 Furnace Model TUD060R9V3K4
    w/ 12 speed blower with 825 CFM maximum
    Return Plenum:
    R1 (D=10-IN, L=1.5-FT)
    R11 (D=8-IN, L=3.5-FT, A=535 SQ-FT, V=4600 CU-FT)
    *R12 (D=8-IN, L=7-FT, A=180 SQ-FT, V=1430 CU-FT)
    R2 (D=10-IN, L=20-FT)
    R21 (D=8-IN, L=5-FT, A=180 SQ-FT, V=1430 CU-FT)
    R22 (D=8-IN, L=2-FT, A=190 SQ-FT, V=1240 CU-FT)
    **R3 (D=8-IN, L=20-FT, A=320 SQ-FT, V=2560 CU-FT)
    *R12 is positioned at the top of a stairway in a hallway
    ** R3 is the return for the room over the garage
    Supply Plenum:
    S1 (D=12-IN, L=14-FT)
    S11 (D=8-IN, L=26-FT)
    **S111 (D=6-IN, L=6-FT, NORTH SIDE OF A=320 SQ-FT, V=2560 CU-FT)
    **S112 (D=6-IN, L=12-FT, EAST SIDE OF A=320 SQ-FT, V=2560 CU-FT)
    S12 (D=8-IN, L=22-FT, SOUTH SIDE OF A=380 SQ-FT, V=3300 CU-FT)
    S2 (D=8-IN, L=17-FT)
    S21 (D=6-IN, L=11-FT, A=SOUTH SIDE OF 180 SQ-FT, V=1430 CU-FT)
    S22 (D=6-IN, L=13-FT, A=SOUTH SIDE OF 180 SQ-FT, V=1430 CU-FT)
    S3 (D=6-IN, L=24-FT, A=140 SQ-FT V=1200 CU-FT)
    S4 (D=6-IN, L=20-FT, A=8 SQ-FT, V=16 CU-FT)
    S5 (D=6-IN, L=17-FT, A=180 SQ-FT, V=1430 CU-FT)
    ***S6 (D=6-IN, L=6-FT, A=40 SQ-FT, V=320 CU-FT)
    ***S7 (D=6-IN, L=4-FT, A=35 SQ-FT, V=280 CU-FT)
    ** S211 and S212 supply the problematic room over the garage
    *** overheated and overcooled bathroom
    The XV80 was installed 1.5 years ago to replace a 20-year old furnace.
    The furnace Nominal Capacity Output(BTUH) is Stage 1=48,000 and Stage 2=31,200. The furnace is coupled with a XL16i Heat Pump (outside: model 4TWX6024B1000AA, inside: model RXC031S3HPC0) with Nominal Cooling Capacity of 24,000 BTUH. The natural gas furnace to heat pump cut over temperature is set to 45-degreesF so the furnace is most often used for heating. The contractor used flex duct to connect to existing tubular sheet-metal ducting. All returns and supplies are located on the ceiling.
    I registered HVAC-Calc Residential to calculate a current heat loss of 25,000 BTUH and heat gain of 18,000 BTUH on the second floor. I calculate that the added attic insulation will reduce heat loss to 18,000 BTUH and heat gain to 12,500 BTUH.
    After browsing this site, I understand that measurements should be taken by a contractor to confirm airflow and pressure. I'd like to learn enough to understand the implication of the measured values when I get that done.
    I'd appreciate suggestions for questions to ask and answer that will help improve airflow as well as identify qualified contractors.
    Central Kentucky
    Quote Originally Posted by RobG View Post
    Try checking out www.nationalcomfortinstitute.com there is a wealth of information on how your comfort can be improved as well as finding someone in your area.
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.
    Post some pictures ,sounds like a mess,label pictures to match what you have posted.
    The required cfms (aitr flow) for each room has to do with the amount of outside wall,windows ,attic and floor(if not on a slab.
    You can compare those factors and you'll see the room over the garage doesn't have large enough ducts compared to others.
    Use the link in davidr's post.
    You need a room by room man.J,the Man. S ,and then Man. D to redesign the duct system,it takes more then just sq inches of duct comparison to get it right!!
    Huntsville,AL
    then before insulating:
    seal all joints & seams of ductwork,
    be sure bends are smooth with large radius
    have dampers to adjust airflow near the branch takeoffs -- set em per max cfm requirements per load calc -- & required air
    insulate the floor between the gar & bdrm -- I did --
    put any wiring NOT in the middle of the insulation