    Is a sling psycrometer required to acuaratly calculate superheat and subcooling as well as a temperature probe. All we have at work is a laser\infered thermometer . Thanks guys and gals

  2. #2
    Join Date
    Jan 2011
    Location
    Ottawa, Canada
    Posts
    470
    Post Likes
    I'll give the short answer and let the more experienced techs give explanations...

    Yes... Get rid of the infrared. Get one.. And some temp probes.

    Sent from my GSIII on Tapatalk

  3. #3
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,125
    Post Likes
    Quote Originally Posted by andersonbe06 View Post
    Is a sling psycrometer required to acuaratly calculate superheat and subcooling as well as a temperature probe. All we have at work is a laser\infered thermometer . Thanks guys and gals
    An indoor wet bulb temperature is needed to determine the required superheat on a unit using a fixed metering device. As wet bulb temperature increases, more superheat is required.

    On a system using a Thermal Expansion Valve (TXV), the required superheat is maintained by the TXV. That is why on these systems you need to charge by subcooling.

    I too have never been a fan of infrared thermometers for measuring liquid and suction line temperatures.
    Instead of learning the tricks of the trade, learn the trade.

  4. #4
    Join Date
    Oct 2008
    Location
    Winnipeg, Manitoba, Canada
    Posts
    144
    Post Likes
    No. It it not required. In fact i see no use for a sling psycrometer when checking superheat or subcooling. A temperature probe, a gauge and a pt chart is what you need

  5. #5
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,704
    Post Likes
    Quote Originally Posted by andersonbe06 View Post
    Is a sling psycrometer required to acuaratly calculate (target ) superheat and subcooling as well as a temperature probe. All we have at work is a laser\infered thermometer . Thanks guys and gals
    the answer is yes or a wet bulb thermometer and a convoluted mathematical formula.
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  6. #6
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    As others have stated, on fixed metered systems you need to know the wet bulb temperature of the air entering the indoor coil to know the required superheat.

    Rather than a sling psychrometer for measuring the indoor wet bulb temperature, I highly recommend a psychrometer that has a probe that can be inserted through a test hole to measure the wet bulb and dry bulb temperatures where they are entering the indoor coil.
    My current favorite is the Fieldpiece SDP2,

    Most people seem to be unaware that the old standard sling psychrometers are inherently less accurate, rated for +/-5% RH, than most decent digital psychrometers, typically rated at +/-2 or 2.5%RH.

    Retire the IR gun to looking for hot electrical connections/breakers, and big temperature differences in wall sections.

    Many people have come up with, and/or been taught methods that they "never had a problem" with, but in every study that has been done, anywhere from 54% to over 70% of the systems checked during the study were significantly over or under charged by >10%, so clearly there is a big frickin problem...

    Quote Originally Posted by adam_s05 View Post
    No. It it not required. In fact i see no use for a sling psycrometer when checking superheat or subcooling. A temperature probe, a gauge and a pt chart is what you need
    On fixed metered systems, without the wet bulb temperature of the air entering the indoor coil, how do you know what your superheat is supposed to be?

  7. #7
    Join Date
    May 2009
    Location
    Cumming, GA
    Posts
    1,903
    Post Likes
    I use this formula. (Thanks HVACMedic)

    (3 x Entering Wet Bulb - 80 - Outdoor Temp) / 2 = Target Superheat.

  8. #8
    Join Date
    Aug 2007
    Location
    Edmond, Oklahoma
    Posts
    639
    Post Likes
    Quote Originally Posted by andersonbe06 View Post
    Is a sling psycrometer required to acuaratly calculate superheat and subcooling as well as a temperature probe. All we have at work is a laser\infered thermometer . Thanks guys and gals
    All that is required to measure SH / SC is pressure gauges, temperature probes, and P/T chart.

    WB may or may not be required to determine target SH / SC, depending on the unit's charging chart.

  9. #9
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    4,710
    Post Likes
    Anybody tried wrapping a little bit of a wet paper towel around a temperature probe? It was within 1 degree of actual WB.

  10. #10
    Join Date
    Jun 2009
    Location
    South Carolina
    Posts
    686
    Post Likes
    Quote Originally Posted by bobster View Post
    All that is required to measure SH / SC is pressure gauges, temperature probes, and P/T chart.

    WB may or may not be required to determine target SH / SC, depending on the unit's charging chart.
    majority if not all SH charts have wet bulb that i remember looking at lately. And with the DB out and WB inside, superheat can be anywhere from 30 to 6 (or something like that)

  11. #11
    Join Date
    Aug 2001
    Location
    Mechanicsville, Virginia
    Posts
    2,027
    Post Likes
    Quote Originally Posted by bobster View Post
    ...WB may or may not be required to determine target SH / SC, depending on the unit's charging chart.
    FYI, Any chart that doesn't require a wet bulb input assumes 50% indoor relative humidity. Charts that specify pressures can be backward engineered to find the same data as the original superheat chart developed by carrier long ago. It applies to all fixed orifice air conditioners and heat pumps (cooling mode of course). The aforementioned formula was curve fitted from the same data and is very close to dead on for most conditions and many find it to be close enough for all conditions.

    If the superheat is accurately set for the current conditions, future conditions will vary but never be too high to prevent compressor cooling or too low to cause flooding.

    If you need a chart you can have this one

    Originally Posted by adam_s05
    No. It it not required. In fact i see no use for a sling psycrometer when checking superheat or subcooling. A temperature probe, a gauge and a pt chart is what you need

    adam_s05 is correct "It not required". Whether he deserves it or not, nobody's gonna sue him for malpractice.

  12. #12
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,630
    Post Likes
    Quote Originally Posted by penderway View Post
    FYI, Any chart that doesn't require a wet bulb input assumes 50% indoor relative humidity.
    Yeap, they assume 50% RH, and that the space is at, or very near, the normal temperature it is kept.
    Rheem/Ruud, and a few others have charts based on just the outdoor DB and suction pressure, or outdoor and indoor DB.
    Those charts are merely a dumbed down compromise by manufacturers that understand the sad reality of how most "technicians" operate, and came up with a simple charging procedure that will usually not result in to many dead compressors if followed.

    If the RH is significantly higher or lower than 50%, or the space is not at or near normal temperature, the chart cannot be used.

    I pretty much ignore those kinds of charts on split systems, but will go by whatever off the wall weirdness for a charge checking procedure I find on a sticker on a package unit.

    My personal favorite screwy charging procedure is Lennox's subcooling method for fixed orifice systems.

    I'm still:[IMG]http://1.bp.********.com/_wAxDMfEGhoY/TQrlbN4gYXI/AAAAAAAAAXg/kmwztAAni44/s400/Not+Sure+if+serious.jpg[/IMG]

  13. #13
    Join Date
    Aug 2012
    Location
    Gulf Coast
    Posts
    100
    Post Likes
    Quote Originally Posted by mark beiser View Post
    Yeap, they assume 50% RH, and that the space is at, or very near, the normal temperature it is kept.
    Rheem/Ruud, and a few others have charts based on just the outdoor DB and suction pressure, or outdoor and indoor DB.
    Those charts are merely a dumbed down compromise by manufacturers that understand the sad reality of how most "technicians" operate, and came up with a simple charging procedure that will usually not result in to many dead compressors if followed.

    If the RH is significantly higher or lower than 50%, or the space is not at or near normal temperature, the chart cannot be used.

    I pretty much ignore those kinds of charts on split systems, but will go by whatever off the wall weirdness for a charge checking procedure I find on a sticker on a package unit.

    My personal favorite screwy charging procedure is Lennox's subcooling method for fixed orifice systems.

    I'm still:[IMG]http://1.bp.********.com/_wAxDMfEGhoY/TQrlbN4gYXI/AAAAAAAAAXg/kmwztAAni44/s400/Not+Sure+if+serious.jpg[/IMG]
    The package unit comment took me back a few hours today when tge boss told me to figure how much freon is in the equipment at one of our accounts.... Would be nice if they were packs, but since tgey are all 5-30 ton splits with varying line sizes... I may be figuring for a while! Ill go gst rough lineset distances tomorrow and calculate what ammount is supposed to be there...