Results 14 to 24 of 24
    Feb 2013
    In a house with windows and doors on it.
    Interesting thread, We had same problem with an X13 on a York Unit. Constant run. 16 Go Backs To Cst. House. Still never fixed problem.
    Feb 2013
    Why does the blower run continuously without a call from the thermostat on this York packaged unit?
    This usually indicates a limit has tripped.
    Jan 2013
    Western Ky
    sounds like it could be bad module, never had one run constant though usually wont run at all, most x13 failures ive run across have been right at the start of cooling season or right at the start of heating season something with the humidity and moisture getting in the modules
    Feb 2013
    I've already replaced module. Same problem, constantly after call for cool ends. Sometimes Ill go out there and the system is off and the blower is on. I'm trying to understand why the limit would cause the blower to constantly run.
    Quote Originally Posted by mr.charles View Post
    Its a safety to cool off the heat exchanger.
    Feb 2013
    Its not a furnace
    To cool off the electric resistance heaters in a heat pump or electric furnace.
    Arizona
    I know you said it runs on any 24v tap, but does it change speeds as you do this?
    Jan 2012
    Arrowhead Stadium
    I have had problems with nest stats that have switches in the sub base.
    Anchorage Alaska / Seattle WA
    Whatever is controlling your motor has failed.... either the fan relay has welded closed or the board scr has failed shorted.
    Jul 2012
    Ashland, VA
    I was doing a startup on a Carrier system once, fan motor would run constantly. Easy solution, the plug on the board was connected backwards. I flipped it around the right way and everything worked perfectly.