Thread: Leak Checks and Pressure Tests

  1. #1
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes

    Leak Checks and Pressure Tests

    I have read a few posts on here stating that to check R410A systems techs run the nitrogen up to 350 psig. Some say 200 psig and I haven't really seen anything yet about R22 (I usually go with the max test pressure on the template, if I can). My problem is my regulator will only give me about 165 psig max. I brought it up to the service manager today and he said he might could get the owner to buy new ones capable of the higher ranges but he wanted something in writing that there was a benefit to the higher pressure testing. I have no idea for where to find such a document, and our service manager doesnt know anything about HVAC, so me trying to explain that testing at closer to the operating pressures did not work. Any body have a clue where I could find something to print and show?
    "If you've eliminated all other possibilities whatever remains must be the truth."

  2. #2
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    In my experience, a leak will show itself at any test pressure, I think guys use higher pressures so a leak will be exposed faster and is easier to find.

    Take gas lines for example. A typical residential line is tested at 15psi. If there is a leak, it will show.
    Try using a digital pressure gauge when testing, it makes pressure drops easier to see.

  3. #3
    Join Date
    May 2012
    Location
    Upper Michigan
    Posts
    3,588
    Post Likes
    Look in an install manual, the last few I did say right in them the pressure to test at which is 300ish, it's been awhile lol. so the Benefit is your doing it right and you can sleep at night.

  4. #4
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    3,341
    Post Likes

  5. #5
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    That was actually the post that motivated me try an get them to get different regulators because I just had a job with a 410 unit and the only leak I could find was a very small one at the suction line isolation valve but I am not 100% sure that leak was adequate for explaining the system needing recharging every year, especially since it has a cap (although the caps are crap and dont have o-rings). I hate second guessing myself and I will worry about that dang job for a year now.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  6. #6
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,432
    Post Likes
    use a vacuum gauge like the bluvac....you'll know immediately if you have a leak...tiny or not.

  7. #7
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    1,041
    Post Likes
    I am not a scientist, but I would imagine it would depend on the actual structure of the R-410a compound molecule as compared to the nitrogen molecule. If I could I would use a 50 psi charge of helium. As it is the lightest gas available that is still an inert gas (non-flamable) . Many manufactures use helium for factory leak test, especially in absorbers and we know how tight they have to be. _GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  8. #8
    Join Date
    Nov 2011
    Location
    St. Louis
    Posts
    7,473
    Post Likes
    Quote Originally Posted by syndicated View Post
    In my experience, a leak will show itself at any test pressure, I think guys use higher pressures so a leak will be exposed faster and is easier to find.

    Take gas lines for example. A typical residential line is tested at 15psi. If there is a leak, it will show.
    Try using a digital pressure gauge when testing, it makes pressure drops easier to see.
    15 PSI for a resi gas line? How many leaks do you find versus the one you create? Did you mean 15" WC?

  9. #9
    Join Date
    Jan 2013
    Posts
    1,179
    Post Likes
    Quote Originally Posted by hurtinhvac View Post
    15 PSI for a resi gas line? How many leaks do you find versus the one you create? Did you mean 15" WC?
    he means 15 psi. It's no the supply pressure.
    Any pipe can hold that pressure and you won't cause leaks.

  10. #10
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    This should answer all your questions...straight from Copeland's mouth.
    http://lvhvac.com/cope_bulletins/1177.pdf

  11. #11
    Join Date
    Feb 2013
    Location
    Summerville SC
    Posts
    117
    Post Likes
    Quote Originally Posted by Joehvac25 View Post
    Look in an install manual, the last few I did say right in them the pressure to test at which is 300ish, it's been awhile lol. so the Benefit is your doing it right and you can sleep at night.
    I believe tranes hyperion air handlers say 150 psi so don't use there documents haha. but I believe either Mitsubishi or fujitsus manual says a minimum of 200 psi. you always can ask the famous rundawg for some document I haven't seen anything he didn't have or couldnt find!
    "only 2 tools any man needs is wd40 and duct tape. if it moves and it shouldn't use the duct tape. if it doesn't move and should, use the wd40" -unknown

  12. #12
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Prime example today, went on a no cool call this morning, found the unit had about 5 psi of refrigerant left in it, R410a. I added about half a pound of 22 and run the nitrogen in as high as my regulator would let it, 165 psi. I searched for a leak for about an hour and a half and found nothing. went back to the condenser and gauges still said 165. Now after the talk I gave the customer why it was important to do a leak check for $xxx/hour, I had to go back and explain I could not find one, it must be small, recommended injecting dye. So from this I could determine:

    1) Since the machine was practically empty, it must have a leak.
    2) If it held 165 psi nitrogen for 90 minutes without budging, it must not leak at 165 psi
    3) the unit held a 450 micron vacuum for 10 minutes, so based on number one that means nothing.
    4) To properly check a 410 system for leaks, you have to be able to put at least as much pressure on it as it operates at.

    If it were not for discovering the system empty, I would have said it had no leaks.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  13. #13
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    Quote Originally Posted by jmsmars1 View Post
    I have read a few posts on here stating that to check R410A systems techs run the nitrogen up to 350 psig. Some say 200 psig and I haven't really seen anything yet about R22 (I usually go with the max test pressure on the template, if I can). My problem is my regulator will only give me about 165 psig max. I brought it up to the service manager today and he said he might could get the owner to buy new ones capable of the higher ranges but he wanted something in writing that there was a benefit to the higher pressure testing. I have no idea for where to find such a document, and our service manager doesnt know anything about HVAC, so me trying to explain that testing at closer to the operating pressures did not work. Any body have a clue where I could find something to print and show?
    what leak detector are you using?

    and, your company hired a SERVICE MANAGER that doesnt know anything about HVAC?????????

    what a great idea..............
    my boss thinks its possible to repeal the laws of physics

  14. #14
    Join Date
    Feb 2006
    Location
    FL
    Posts
    574
    Post Likes
    I was wondering about that, a service manager that doesn't know the trade hes managing. Good luck.

  15. #15
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Here's what I do, take it or leave it.

    If no history is available on the unit I just recharge it and tell the customer that I put 'x' amount of refrigerant in and that we don't know what the situation is as far as leaks until we have some more info, depending on how long it takes for you to come back(if at all) you now know an approximate leak rate. 3 years, slow leak. 3 months, fast leak. If 3 months add nitro, I go up to 150psi on both 410-a and r-22 but I use DC gauges which go down to tenths and give it a good 30 minute or longer pressure test, depends on if I can run more calls while it sits. I've done 24 hours before. If its barely leaking check schraders and service valves first , found a lot of schraders leaking slowly. If you check the whole system and nothing is showing anything but the evap coil(assuming copper) is looking rough then it's most likely the evap coil.

  16. #16
    Join Date
    Feb 2010
    Location
    Calgary, Alberta
    Posts
    1,679
    Post Likes
    Quote Originally Posted by hurtinhvac View Post
    15 PSI for a resi gas line? How many leaks do you find versus the one you create? Did you mean 15" WC?
    Sched 40 black pipe is rated to 125 psi.
    Code mandates pressure tests on res. gas lines to be done at a minimum of 15 psi.

    Soo..... What are you talking about?

  17. #17
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Quote Originally Posted by ch4man View Post
    what leak detector are you using?

    and, your company hired a SERVICE MANAGER that doesnt know anything about HVAC?????????

    what a great idea..............
    I am using a Robinair 16600, and Big Blu soap bubbles. He used to work at the gas company selling fireplaces is what i was told, he is more there for sales than anything else, gets our restock for the vans, sometimes, handles vehicle maintenance, sometimes, if you fuss enough. Been trying to get the oil changed in my van for 7000 miles now...

    I know my detector isn't the best and I would like another one, but we are required to purchase our own tools and barely make a living wage. The only things the company supplies are: van, torch, nitrogen regulator, recovery machine. I am the only person in our company that even owns a vacuum gage.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  18. #18
    Join Date
    Nov 2007
    Location
    Tucson, AZ
    Posts
    265
    Post Likes
    I had an r-22 unit one time that was low. oil all over the place. thought hmm easy find charge it with nitrogen 150 psig then 250 still held. finally 350 and still held. I was stumped until I started moving pipes then I heard the little hiss. found it at the discharge of the compressor after the 90 bend no joints all one tube.. must of been getting hot due to a bad cond fan and then overheated that piece..

  19. #19
    Join Date
    May 2011
    Location
    Western, KY
    Posts
    3,430
    Post Likes
    Quote Originally Posted by syndicated View Post
    Sched 40 black pipe is rated to 125 psi.
    Code mandates pressure tests on res. gas lines to be done at a minimum of 15 psi.

    Soo..... What are you talking about?
    We have a municipality that requires us check our gas lines at 60psi!!!

    The other ones require 14-20psi.

  20. #20
    Join Date
    Jul 2002
    Posts
    1,790
    Post Likes
    www.bacharach-inc.com/h-10g.htm

    I can find ANY leak with this leak detector at 30 psi. My old boss would buy cheap detectors because he'd bill customers for multiple refills. When I got this I used to take it outside, let it warm up, set it very sensitive, and when I walked into a store I could detect if there was a leak anywhere in the building. NO KIDDING!

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •