    Duct mastic

    What size gap can duct mastic be used up to? Can I use it on a gap about a 1/2"?

    If I can't use mastic what should be used to fill that gap, silicon?

    It's to seal off a return where the top has sagged down from the joist.

  2. #2
    Join Date
    Sep 2002
    Location
    Northeast Ohio
    Posts
    4,842
    I would try to push the duct back into place and fasten it first. If this is not possible, fill the gap with light gauge sheet metal then seal with mastic.
    A good HVAC tech knows how, an educated HVAC tech knows why!

    DEM


  3. #3
    Join Date
    Jun 2011
    Location
    SW Ohio
    Posts
    224
    I will have to go get some light metal then because this is the top side of the return where it runs perpendicular to the joist so no way of pulling the top up.

  4. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,046
    Mastic tape the cover with mastic or sheet metal and mastic.

  5. #5
    Join Date
    Jun 2011
    Location
    SW Ohio
    Posts
    224
    What about using that heavy metal foil tape (May be mastic tape?) with matic over that? I have some of that stuff when I built my attic box to block off my pull down stairs for insulating it.

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,046
    If its butyl backed foil tape it will work well (putty like about 1/16" thick) regular foil tape would be ok with a thick layer of mastic as long as you can get it to stick. Mastic tape (butyl backed foil tape) will adhere to just about anything.

  7. #7
    Join Date
    Jan 2006
    Location
    McQueeney, Texas
    Posts
    3,865
    It will need insulating afterwords of course, to prevent sweating or heat gain/loss.

  8. #8
    Join Date
    Jun 2011
    Location
    SW Ohio
    Posts
    224
    Quote Originally Posted by walterc View Post
    It will need insulating afterwords of course, to prevent sweating or heat gain/loss.
    This is in a finished basement.

    This stuff: http://www.homedepot.com/p/Nashua-Ta...cked+foil+tape

  9. #9
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,046
    No, this stuff Removed link to direct purchase site.
    Last edited by beenthere; 04-27-2013 at 09:58 AM.

  10. #10
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    7,046
    Sorry BT, hardcast 1402 is mastic tape.

  11. #11
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,188
    that's my tape of choice 1402 mastic Hardcast brand!!

    the link is just foil with sticky backing...not mastic.

    you can use nylon webbing pushed into first layer
    of mastic & then mastic over it.
    but you should give it 24 hours to dry & recoat
    it with mastic.

    can you show us a picture?

    best of luck.
    The cure of the part should not be attempted without the cure of the whole. ~Plato

  12. #12
    Join Date
    Jun 2011
    Location
    SW Ohio
    Posts
    224
    Here are two pics where it has a larger gap.




  13. #13
    Join Date
    May 2004
    Location
    south louisiana
    Posts
    3,188
    that is the top of the return & a joist above it?
    why seal return to joist??
    it looks like return is independent of joist...
    and not a part of the return.
    am I just seeing this wrong??
    The cure of the part should not be attempted without the cure of the whole. ~Plato

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event