Results 1 to 5 of 5
  1. #1
    Join Date
    Apr 2013
    Posts
    3
    Post Likes

    question on refrigerant charge of water cooled screw process chiller

    When the compressor runs at full capacity the liquid line sight glass is full and when the slide valve reduces compressor capacity the liquid line sight glass drops to half and even 1/4 full. I have seen flashing in the sight glass with reciprocating compressors running unloaded and clear up when fully loaded, so just wondering if this is normal with screw compressors or the system is low on refrigerant? The condenser water temp fluctuates it is not heated it is regulated with a water regulator actuated by system head pressure, 134a refrigerant which was running around 116, psi back pressure was 11 psi with 36 deg chilled fluid compressor running approx 50 percent capacity. Any input would be appreciated; thanks

  2. #2
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,177
    Post Likes
    suction sounds pretty low

  3. #3
    Join Date
    Apr 2013
    Posts
    3
    Post Likes
    Thread Starter
    yes a little low but very steady as it increases capacity it does not dive....capacity is being controlled by suction pressure

  4. #4
    Join Date
    Jan 2011
    Posts
    1,580
    Post Likes
    Quote Originally Posted by r404a View Post
    suction sounds pretty low
    X2

    That pressure corresponds to about 6*F with a product temperature of 36*F. That doesn't sound right to me.

    As for the sight glass showing different conditions...the screw compressor is a positive displacement compressor just like a recip. But just because the sight glass is full doesn't mean you are correctly charged. You need to know what the manufacturer wants for sub-cooling and superheat under full load conditions.

  5. #5
    Join Date
    Apr 2013
    Posts
    3
    Post Likes
    Thread Starter
    Thanks for the info you are absolutely correct system was low on refrigerant determined by only 1 deg subcooling mfg recommended 10 - 15 at full capacity. Thanks again

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.