    Does the drive itself accept your fieldbus? Lon? Which can tell you the speed?

  2. #15
    Join Date
    May 2006
    Location
    Greater Seattle Area
    Posts
    537
    Post Likes
    Do the VFD's have a Lonworks interface option card installed or available? A lot have this option now and perhaps that would be a simpler solution since you get a multitude of data out of it to utilize for speed (Hz, Amps, Ref Hz as seen by drive etc.)

  3. #16
    Join Date
    Apr 2006
    Location
    Columbus, Ohio
    Posts
    1,011
    Post Likes
    Thread Starter
    Quote Originally Posted by controlgeek View Post
    Do the VFD's have a Lonworks interface option card installed or available? A lot have this option now and perhaps that would be a simpler solution since you get a multitude of data out of it to utilize for speed (Hz, Amps, Ref Hz as seen by drive etc.)
    That is a good thought. I believe they are Danfoss VFDs. I will look into that as a option. That would be a lot more accurate.

    Thanks for all of the replies.
    J. King

  4. #17
    Join Date
    Mar 2007
    Posts
    488
    Post Likes
    Sample and hold. I've used it for years for static pressure sequences and it works pretty solid.