    high pressure switch and solenoid valve

    hi
    i have lg 24000 btu split ac unit
    there is high pressure switch and solenoid valve
    Name:  Snap_2013.04.25_20h00m01s_001.jpg
Views: 350
Size:  40.4 KB
    the both the solenoid valve and hi pressure switch are wired to the outdoor fan
    the solenoid installed to the suction pipe of condenser
    the hi press switch connect between capillary tube and the discharge of the compressor
    what is the utility of them

  2. #2
    Join Date
    May 2010
    Location
    Brooklyn, NY
    Posts
    99
    solenoid valve opens when there's a call for cool, and high pressure switch trips when the discharge pressure is too high, the reason it they're in series is so that if the high pressure switch trips, the solenoid valve will be closed, that way no refrigerant flow, and causing a stop to the compressor.

  3. #3
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,134
    Quote Originally Posted by EEAllen View Post
    solenoid valve opens when there's a call for cool, and high pressure switch trips when the discharge pressure is too high, the reason it they're in series is so that if the high pressure switch trips, the solenoid valve will be closed, that way no refrigerant flow, and causing a stop to the compressor.
    this happen in heating mode
    or cooling

  4. #4
    Join Date
    May 2010
    Location
    Brooklyn, NY
    Posts
    99
    Both, btw why does ur profile said hvac engineer?

  5. #5
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,134
    Quote Originally Posted by EEAllen View Post
    Both, btw why does ur profile said hvac engineer?
    yes
    i am hvac engineer
    but my knowledge is not so good
    because of bad state in iraq
    and about the thread
    before i asked the question
    i thought the hi pressure switch connected in series with solenoid valve and outdoor fan
    so in heating mode
    when the pressure reach hi level the hi pressure switch will stop the outdoor fan to decrease the pressure
    and protect the compressor
    but the solenoid valve i know it work as hot gas bypass to prevent the freezing of evaporator but that happen in cooling mode
    so why they connect the hi pressure to that valve
    thank you for your help

  6. #6
    Join Date
    May 2010
    Location
    Brooklyn, NY
    Posts
    99
    the purpose of the solenoid valve is to just let the refrigerant flow. I have not look into the mechanical part of split ac, but they should work the same as all refrigeration systems. So if the pressure of the discharge gets too high, the high pressure switch will trip, causing the solenoid valve to close. Without the flow of refrigerant, the compressor will shutdown due to low on pressure. I wasn't able to find the mechanical side of these split AC units, if you have any, I would appreciate it if you share

  7. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,797
    kefah. Because of your extreme high ambient temps. They may be using that set up to prevent high head pressure in cooling mode. But that diagram shows the solenoid tapped off the compressor's common.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,134
    Quote Originally Posted by beenthere View Post
    kefah. Because of your extreme high ambient temps. They may be using that set up to prevent high head pressure in cooling mode. But that diagram shows the solenoid tapped off the compressor's common.
    so the hi pressure will stop the compressor
    but the solenoid valve will prevent the freeze of evaporator or what

  9. #9
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,134
    Quote Originally Posted by EEAllen View Post
    the purpose of the solenoid valve is to just let the refrigerant flow. I have not look into the mechanical part of split ac, but they should work the same as all refrigeration systems. So if the pressure of the discharge gets too high, the high pressure switch will trip, causing the solenoid valve to close. Without the flow of refrigerant, the compressor will shutdown due to low on pressure. I wasn't able to find the mechanical side of these split AC units, if you have any, I would appreciate it if you share
    Name:  Snap_2013.04.26_23h55m17s_001.jpg
Views: 570
Size:  48.2 KB

  10. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,797
    Quote Originally Posted by kefah View Post
    so the hi pressure will stop the compressor
    but the solenoid valve will prevent the freeze of evaporator or what
    Won't stop the compressor. It gets its power from teh compressor common wiring. but it doesn't beak the connection.

    Pic looks like a hot gas bypass.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  11. #11
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,134
    Quote Originally Posted by beenthere View Post
    Won't stop the compressor. It gets its power from teh compressor common wiring. but it doesn't beak the connection.

    Pic looks like a hot gas bypass.
    so when hi press switch work during hi head pressure
    it will bypass the freon to evaporator to decrease the load or what

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,797
    Check the pressure witch rating.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #13
    Join Date
    Aug 2012
    Location
    Iraq
    Posts
    1,134
    Quote Originally Posted by beenthere View Post
    Check the pressure witch rating.
    what you mean

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event