Results 1 to 13 of 28
    Aug 2012
    Iraq
    high pressure switch and solenoid valve
    hi
    i have lg 24000 btu split ac unit
    there is high pressure switch and solenoid valve
    the both the solenoid valve and hi pressure switch are wired to the outdoor fan
    the solenoid installed to the suction pipe of condenser
    the hi press switch connect between capillary tube and the discharge of the compressor
    what is the utility of them
    May 2010
    Brooklyn, NY
    solenoid valve opens when there's a call for cool, and high pressure switch trips when the discharge pressure is too high, the reason it they're in series is so that if the high pressure switch trips, the solenoid valve will be closed, that way no refrigerant flow, and causing a stop to the compressor.
    Aug 2012
    Iraq
    Quote Originally Posted by EEAllen View Post
    this happen in heating mode
    or cooling
    May 2010
    Brooklyn, NY
    Both, btw why does ur profile said hvac engineer?
    Aug 2012
    Iraq
    yes
    i am hvac engineer
    i thought the hi pressure switch connected in series with solenoid valve and outdoor fan
    so in heating mode
    when the pressure reach hi level the hi pressure switch will stop the outdoor fan to decrease the pressure
    and protect the compressor
    but the solenoid valve i know it work as hot gas bypass to prevent the freezing of evaporator but that happen in cooling mode
    so why they connect the hi pressure to that valve
    thank you for your help
    May 2010
    Brooklyn, NY
    the purpose of the solenoid valve is to just let the refrigerant flow. I have not look into the mechanical part of split ac, but they should work the same as all refrigeration systems. So if the pressure of the discharge gets too high, the high pressure switch will trip, causing the solenoid valve to close. Without the flow of refrigerant, the compressor will shutdown due to low on pressure. I wasn't able to find the mechanical side of these split AC units, if you have any, I would appreciate it if you share
    kefah. Because of your extreme high ambient temps. They may be using that set up to prevent high head pressure in cooling mode. But that diagram shows the solenoid tapped off the compressor's common.
    Aug 2012
    Iraq
    so the hi pressure will stop the compressor
    but the solenoid valve will prevent the freeze of evaporator or what
    Aug 2012
    Iraq
    Quote Originally Posted by kefah View Post
    Won't stop the compressor. It gets its power from teh compressor common wiring. but it doesn't beak the connection.
    Pic looks like a hot gas bypass.
    Aug 2012
    Iraq
    so when hi press switch work during hi head pressure
    it will bypass the freon to evaporator to decrease the load or what
    Check the pressure witch rating.
    Aug 2012
    Iraq
    what you mean