    Line set

    Will a 3 ton unit work w/a 5/8" line set? If so what are ramifications, compressor damage, lower eff, etc?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,749
    5/8 liquid line seems a little large.

  3. #3
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,281
    Thread relocated to AOP

  4. #4
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    310
    I assume you are talking about a ⅝ suction line. That would be undersized for a 3 ton application. You would want to use a 3/4" suction line and a 3/8 liquid line.

  5. #5
    I know 3/4" is spec, but existing in wall is 5/8 can't replace so will 5/8 damage 3 t unit or will it even work. Another option is I have a redundant 5/8 line is it possible to combine these or would that be to much capacity?

  6. #6
    Join Date
    Mar 2013
    Location
    Joplin,Missouri
    Posts
    310
    I would not want to comment if the 5/8 would work or not. It may function, it may not but it would not have near the proper capacity I don't like to give advice to people when I'm not positive what the outcome would be.sorry I would just open the wall and change the lines and make it right

  7. #7
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    As long as it is not a really long line set, a 5/8" suction line is just fine with a 3 ton R-410A system, but there will be capacity loss.

    How lone of a run is it?
    If more government is the answer, then it's a really stupid question.

  8. #8
    25' to 30'. So all I will loose is a small % of eff? A 5/8-1/4" line set won't harm unit?

  9. #9
    Sorry about that line set is 5/8-3/8"

  10. #10
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Quote Originally Posted by Tim sample View Post
    25' to 30'. So all I will loose is a small % of eff? A 5/8-1/4" line set won't harm unit?
    Assuming a few LR 90º fittings, your looking at loosing in the neighborhood of 500 btuh of the systems capacity, vs around 150 btuh loss with a 3/4 inch suction line, so around 350 btuh difference.
    If the line is in good shape, its not worth chasing that 1% difference in total capacity, as you would likely never see a payback in the life span of the system.
    The higher refrigerant velocity in the 5/8" suction line will result in more reliable oil return, so could potentially actually extend the life of the compressor.

    You didn't mention the 1/4" liquid line in the OP. That is a no go for a 3 ton system, even with a short line set, due to the pressure drop.
    5/16 would be the minimum.
    If more government is the answer, then it's a really stupid question.

  11. #11
    Join Date
    Aug 2010
    Location
    West Monroe, LA
    Posts
    1,535
    I would say more then lickly if you have 5/8 suction line then your liquied line will be 5/16 which might appear to be 3/8 really hard to tell then apart sometimes. Will it work yes but expect btu loss.

    I would confern that you do have 5/8 and 3/8 and get installer to see what the loss will be and if you have 5/8 and 5/16 same applys you are pushing the limits of the line set. If its 1/4 on the liquid line then it will not work propely and all kind of problems can occur.

    Installer needs to run this through pipeing software and see what the loss is or will be. Only real way to know for sure.

  12. #12
    Thank u guys for the info,I'm going for it. Don't want expense and mess of 3 floors of Sheetrock tear out and replacement to change line set. It is 5/8-3/8"

  13. #13
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Quote Originally Posted by Tim sample View Post
    It is 5/8-3/8"
    Then you are good to go.
    If more government is the answer, then it's a really stupid question.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event