    Typical Chiller Parameters

    Hi All...

    I am from INDIA, Delhi Specifically.
    1) I want to know what steps i should follow to get the best efficiency from my chiller machines. The capacity is 350 Tr with ambient temperatures b/w 34 to even 40 Deg C (93 deg F to 115 Deg F)and humidity is usually bearable (24 - 30 %).
    2) What are the chiller plants typical parameters that should be maintained to get the best efficiency.

    could any one please explain in detail....

    Thanks and Regards

  2. #2
    Join Date
    Apr 2013
    Location
    Delhi, INDIA
    Posts
    2
    and the compressor is screw type water cooled plant..

  3. #3
    Join Date
    Jul 2003
    Location
    Orange County N.Y.
    Posts
    1,176
    Quote Originally Posted by Animax007 View Post
    and the compressor is screw type water cooled plant..
    I don't think that there is really much to detail once the chiller is up and running. Clean tubes, clean water, clean towers, the cooler the condenser water is (to minimum temp) the more efficient the chiller will run, repair refrigerant leaks, have the oil checked yearly for contaminents/metals/etc., change oil filter yearly (other opinions vary on this), preventive maintenance is always your friend.