    Head scratcher

    Good evening all. Just did a Emerson digital scroll compressor change out on a 16 ton Daikin after a burn out. Change out went well until vacuum pull down. Before vacuum a nitrogen charge and leak check was done and no leaks found. Vacuum pull down began to get erratic at about 700micron. Check all Schrader caps and valves, everything is tight and no apparent leaks. Figure maybe there was moisture in the system so continue to pull and finally after about four hours finally reach about 590 micron. Obviously something is still not right so I go to the air handler and check to see if a vacuum is actually being pulled through the entire line set. So here we go, after about 17 feet on the liquid line there is a one way check valve in line, from there it goes to the filter dryer cores then to a solenoid valve (I opened the valve with a solenoid magnet), from there the line continues to evaporator. This section has no vacuum at all. In fact it's still at atmosphere. Okay so for some reason the vacuum will not pull through the txv...but when charged with nitrogen, nitrogen will flow through the entire system. How the hell is this possible that I can pull a vacuum through both high and low side and this section of pipe stays at atmosphere but nitrogen will flow freely through the system? By the way, the reason for the compressor burn out is still not determined yet I am still investigating to rule out everything prior to starting the new compressor up.

  2. #2
    Join Date
    Jan 2006
    Location
    In a land far, far away
    Posts
    19,523
    Post Likes

  3. #3
    Join Date
    May 2019
    Posts
    397
    Post Likes
    After a burn out you still have the old filter dryer in the system?

    This sounds like a major investment of someone's dollars.
    I would probably even change the TXV and any filter driers.

    Many TXV's have a reverse flow valve set up that may be adding to the confusion, especially if junk from a burn out is in it.

  4. #4
    Join Date
    Aug 2021
    Posts
    4
    Post Likes
    Thread Starter
    No, I replaced the filter dryers. Should have said that. We did think of the reverse flow valve set up but then the reverse flow should have the same effect on the nitrogen as well as the vacuum wouldn't it? That's where the confusion is.

  5. #5
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    RTU? VRV?

  6. #6
    Join Date
    Aug 2021
    Posts
    4
    Post Likes
    Thread Starter
    RTU . Daikin RCS unit

  7. #7
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    You replaced Factory FD or Field Installed FD's?

  8. #8
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,438
    Post Likes
    Which part of the line was at atmospheric?

    The section between the check valve and the LLSV?

    Or

    The section from the LLSV to the TXV?

    Also, is there a relief in the section between the check valve and LLSV? Should have one that is piped back to another section of line open the rest of the system.

  9. #9
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    How do you know nitrogen will flow through the entire system?

    Where are you pulling vacuum?

    Where are you measuring vacuum?


    Sent from my iPhone using Tapatalk

  10. #10
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    Just a thought...

    I am not familiar with this system but, is it possible that the valve will open with pressure and close down if it does not see pressure? that is about the only way that I could see this happening.

    Or maybe with enough nitrogen pressure it forced the valve open and the vacuum can't do that.

    Sorry if I am way off base here but found this thread interesting and jut posted what seems logical to me.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •