Question; klixon switch and fan delay probe
This is a question thats been buggin me for a while so what better place to ask it...
On a danfoss controlled system the fans on a freezer evap are delayed mechanically/electrically by the klixon, yet the evap coil also has a fan delay temp probe to delay the fans by the danfoss controller. Does any one know the point to this?
Does one protect against one thing while the other allows for something else? or something? I dont understand the use of both.
-
02-13-2007, 10:24 AM #2
Typically one is defrost terminate and the other is fan delay.
-
02-14-2007, 12:32 AM #3
Some manufactures fit these thermostats as standard equipment to their low temperature unit coolers, I think the trend is for electronic controls.
If the thermostats are still connected I would suggest they are there as a fail safe.
If I was doing the install I would remove them, as the controller has temperature termination of the defrost with maximum time over-ride, drip time and temperature start for the fans.
All this can be achieved with a paragon defrost timer at greater cost.
just my opinion
-
02-14-2007, 03:20 AM #4
Regular Guest
- Join Date
- Feb 2007
- Posts
- 48
-
02-14-2007, 08:54 AM #5