    Question temp rise formula

    Hi, does anyone have a temp rise formula for 3 phase to calculate CFM on an AHU. Thanks for any help, John

  2. #2
    Join Date
    Dec 2002
    Location
    Titusville Florida
    Posts
    337
    cfm= heater btu's / delta t X 1.08 you can use the long formula with 1.73, but this will get you in the ballpark

  3. #3
    Join Date
    Feb 2007
    Location
    pa
    Posts
    41
    Thanks for the formula, is there one to get the BTU's using the amp draw from the heaters and motor and actual voltage? I used the one for single phase and it can not be correct, is there one for 3 phase? Any help is greatly appreciated, John

  4. #4
    Join Date
    May 2004
    Location
    Los Angeles, CA
    Posts
    1,560
    Dear John E,

    The correct formula for what you are looking for is as follows:

    First find your adjusted BTU/Hr:
    [(V1 + V2 + V3) /3 x (A1 + A2 + A3)/3] x 1.73 x 3.41 = BTU/Hr.

    Then plug it into the following formula for your calculated CFM:
    BTU/Hr. / 1.08 x Delta T = CFM

    Sabre11134, your formula would not only NOT get you in the ballpark, you might miss the entire city to boot!

    Although not asked for, here is the formula for single phase resistant heat:

    First find your adjusted BTU/Hr:
    [(V1 + V2) /2 x (A1 + A2)/2] x 3.41 = BTU/Hr.

    Then plug it into the following formula for your calculated CFM:
    BTU/Hr. / 1.08 x Delta T = CFM

    Hope this helps……..

    Respectfully Submitted,
    John J. Dalton

  5. #5
    Join Date
    Feb 2007
    Location
    pa
    Posts
    41
    That's perfect and exactly what I need. Thank you very much. thank you both for your time, John

  6. #6
    Join Date
    May 2004
    Location
    Los Angeles, CA
    Posts
    1,560
    Dear John E,

    My pleasure my friend…………………

    Respectfully Submitted,
    John J. Dalton CM

  7. #7
    Join Date
    Dec 2002
    Location
    Titusville Florida
    Posts
    337
    Quote Originally Posted by john dalton View Post
    Dear John E,

    The correct formula for what you are looking for is as follows:

    First find your adjusted BTU/Hr:
    [(V1 + V2 + V3) /3 x (A1 + A2 + A3)/3] x 1.73 x 3.41 = BTU/Hr.

    Then plug it into the following formula for your calculated CFM:
    BTU/Hr. / 1.08 x Delta T = CFM

    Sabre11134, your formula would not only NOT get you in the ballpark, you might miss the entire city to boot!

    Although not asked for, here is the formula for single phase resistant heat:

    First find your adjusted BTU/Hr:
    [(V1 + V2) /2 x (A1 + A2)/2] x 3.41 = BTU/Hr.

    Then plug it into the following formula for your calculated CFM:
    BTU/Hr. / 1.08 x Delta T = CFM

    Hope this helps……..

    Respectfully Submitted,
    John J. Dalton
    sounds like you are going to get the same figures with out going three miles to get the fact 1 kw equals 3413 btu's. looks like a big ego here

  8. #8
    Join Date
    May 2004
    Location
    Los Angeles, CA
    Posts
    1,560
    Dear Sabre11134,

    Regarding your posted formula and comments:

    “…you can use the long formula with 1.73, but this will get you in the ballpark…”

    Without using the three phase conversion constant (1.73) that you said was not needed to get you in the ballpark, your formula would only give you an answer that was 57.8% of the correct one……..I ask you this question sir:

    Is an answer off by over 42% in the ballpark to you?

    By the way, if I had an ego, then I would have listed the three phase constant as 1.7320508 +/- 1,000,000th.

    Respectfully Submitted,
    John J. Dalton

  9. #9
    Join Date
    Jul 2006
    Location
    Canada
    Posts
    60
    Here is a quick easy question for your ego's. What's is the easist way to get your delta T, is it just simply taking the difference from return and supply

  10. #10
    Join Date
    May 2004
    Location
    Los Angeles, CA
    Posts
    1,560
    Dear Northwestmechanic,

    Sabre11134 was the one that brought up egos, not me. As far as egos are concerned, based on the complexity of this industry and the growing lack of knowledge I find I don’t poses, I’m not surprised by the mistakes I make in my job, but rather shocked that I don’t more of them.

    As for your “quick and easy question”……………the answer is no, it is not as simple as“…taking the difference from return and supply…” You have to get the air entering and leaving the electric heater as close as you can to the heater, while at the same time making sure you are not in a line of sight between the heating elements and your temperature sensor, least radiant heat would give you a false reading (higher reading).

    Your comments…………..

    Respectfully Submitted,
    John J. Dalton CM

  11. #11
    Join Date
    Jun 2006
    Posts
    147
    CFMx1.08x Delta -T air =BTU/ Hr. So what is the required airflow for a 10kw duct heater to keep it from riding limits? If I use this formula based on figures obtained from the duct heaters temp rise and and CFM ? Will I get 10 kw regardless of air volume? I know I'm not the sharpest tack in the box. Thanks, Ken

  12. #12
    Join Date
    May 2004
    Location
    Los Angeles, CA
    Posts
    1,560
    Dear Joken,

    Regarding your posted question:

    “…So what is the required airflow for a 10kw duct heater to keep it from riding limits?..”

    Although the range of temperature rise through a normal duct heater will differ drastically based on the application, the type of heating element used in the heater, the type, location, and range of high limit controls, and the heater manufacturer, an acceptable range is between 20 and 40 degrees F for most conventional HVAC uses. If we were to take a mid-range of 30 degree F as our target point we could then perform the following calculation to determine our target CFM value:

    (10,000 w x 3.41) / 30 degrees F x 1.08 = 1,052 CFM

    Hope this helps…………………

    Respectfully Submitted,
    John J. Dalton CM

  13. #13
    Join Date
    Jun 2006
    Posts
    147
    John, If answering these questions is your job, you are doing it well and I thank you. I actually only have 500cfm which equates to around a 60 degree rise. I need that much for reheat when the RTU is cooling. I'm trying to make a poor design work. Do you have an opinion as to wheather the reheats will hold up. 145 limit on the bottom 240 center and top. I guess time will tell since they need to be that large. Thanks again, Ken

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event