    Angry trane tud080 circuit board problem

    Error code shows check ignitor! tested ignitor and shows good. can bypass control board and start furnace. Thought it was board maybe even relay in board! replaced board and still same thing! Checked all safty switches checked pressure switch and still show's check ignitor. Also checked plarity to ignitor. If i put direct power to the induce motor and hot surface ignitor they will come on and stay on. so I know it is not the ignitor or the motor.
    Eny ideas???
    Last edited by redvette30; 02-13-2007 at 07:33 AM.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    3,373
    i am not real familiar with this unit, however, i do know that some brands require that the 120 VAC polarity be correct. after ignition, they will drop out the neutral and leave the 120 hot connected as the flame proving voltage source. if you drop out the hot (since the polarity is reversed), you end up dropping out the whole circuit.
    The weak aren't destroyed by the strong.
    The weak are destroyed by the under-estimated.

    I know a famous song that ends in 'my nose'. The artist is dead. Know who?

  3. #3
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,212
    Just how did you go about testing ignitor?????????

    When you bypass the board, you bypass everything.........

    Stopp!!!!!!!!!!!!!!!and call someone to fix it
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  4. #4
    Join Date
    Jan 2007
    Posts
    60
    For couriosities sake, how did u bypass the board for a gas heater, the ignitione module is built in the board on that particular furnace. Either way
    i would call out a pro to look at it.

  5. #5
    Join Date
    Jul 2006
    Location
    Lancaster,Ohio
    Posts
    464
    What did you replace the board with?
    IcyFlame

  6. #6
    well for bypassing the board I stold main power from incoming transformer.
    to powr the flame ignitor and the exhaust motor. Then on the leaving side of all saftys tested the gas valve and gave it power and system came on!

  7. #7
    Quote Originally Posted by jayguy View Post
    i am not real familiar with this unit, however, i do know that some brands require that the 120 VAC polarity be correct. after ignition, they will drop out the neutral and leave the 120 hot connected as the flame proving voltage source. if you drop out the hot (since the polarity is reversed), you end up dropping out the whole circuit.
    yup did that

  8. #8
    Quote Originally Posted by partsonorder View Post
    For couriosities sake, how did u bypass the board for a gas heater, the ignitione module is built in the board on that particular furnace. Either way
    i would call out a pro to look at it.
    still went thru safty's so don't worry!

  9. #9
    Will try somthing else today

  10. #10
    Join Date
    Feb 2006
    Location
    Temporaly Misplaced in NJ
    Posts
    138
    Try calling a pro.
    Ephesians 2:8,9

  11. #11
    Join Date
    Mar 2004
    Location
    Illinois
    Posts
    6,947
    Sorry redvette but this thread is not appropriate for this forum. Please read the requirements for becoming a pro member and see if you meet them, if so, please apply for pro membership and the issue you are having can be discussed in the proper forum.

    >>>Thread Closed<<<